They give you the length of the ring in the question -- 54m from origin, all the way around the ring and back to origin.

If you were to link line and cpc of one of the legs and take a continuity reading between line and cpc of the other leg you would get (19.51 ÷ 1000) x 54 = 1.05Ω. This is your r1 + r2.

When you join the legs back together as it would be in service, as you rightly said, you have halved the length and doubled the csa.

Half the length, half the resistance -- ½ of 1.05 = 0.52

Double the csa, half the resistance -- ½ of 0.52 = 0.26

so R1 + R2 = (r1 + r2) ÷ 4 = 0.26Ω
 
Last edited by a moderator:
Ok, I think I am begining to understand, but it is the physics that still don't seem to make sense....


Zs is a measurement of the resistance of the complete earth fault path. i.e from the fault, back to the cu and beyond (Ze).
When a fault occurs on a ring circuit, surely the fault takes the path of least resistance?

So for arguements sake if the fault is 30m in on a 50m ring, the fault would travel back down the part of the ring that is 20m away from the CU?

Does that make sense, and is that correct?
 
Ok, I think I am begining to understand, but it is the physics that still don't seem to make sense....


Zs is a measurement of the resistance of the complete earth fault path. i.e from the fault, back to the cu and beyond (Ze).
When a fault occurs on a ring circuit, surely the fault takes the path of least resistance?

So for arguements sake if the fault is 30m in on a 50m ring, the fault would travel back down the part of the ring that is 20m away from the CU?

Does that make sense, and is that correct?

No. The 2 line conductors and 2 cpcs are connected together at the CU, so in effect they are the same conductor. Therefore the fault current would travel both ways around the ring until it gets back to the CU.
 
Think about it this way.

Take your 50m ring. Let's say you have socket outlets at 5m, 10m and 15m on one leg of the ring.

Plug a 13A load into each outlet -- 13 x 3 = 39A.

If the current took the path of least resistance, in this case 15m of 2.5mm² cable with a 27A current-carrying-capacity, it would overload the cable.

**EDIT** And take out the MCB.....eventually :banghead:
 
Last edited by a moderator:
No. The 2 line conductors and 2 cpcs are connected together at the CU, so in effect they are the same conductor. Therefore the fault current would travel both ways around the ring until it gets back to the CU.

Ok, thanks for that.

It was obviously my belief in the 'Path of least resistance' that was clouding my understanding.

Out of curiosity....
If the circuit was a radial one, then the Zs would simply be a calculation of the resistance of the length of the cable from the point of the fault back to the CU. So if we use the original question and say the fault occured at 54m, then the resistance would be 54 X 19.51 /1000 = 1.05 Ohms??

Cheers
 
Ok, thanks for that.

It was obviously my belief in the 'Path of least resistance' that was clouding my understanding.

Out of curiosity....
If the circuit was a radial one, then the Zs would simply be a calculation of the resistance of the length of the cable from the point of the fault back to the CU. So if we use the original question and say the fault occured at 54m, then the resistance would be 54 X 19.51 /1000 = 1.05 Ohms??

Cheers

Correct. Though Zs reading is taken at the last point in a radial circuit or in the case of a ring circuit the highest reading (incl. spurs).
 

Reply to Answers on a postcard please... in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top