Hi all,

Just lately I have seen this quite a few times: a 4 core SWA (cores brown, black, grey and blue) feeds a single phase distribution board. The spare grey conductor has been taped up with green/yellow
tape and used as an earth conductor. The steel armour has been bonded to the metal enclosure of the distribution board.

According to tha colour coding it is a fairly new installation and certainly not good practise.

I always thought you have to run a seperate (green/yellow) wire for earth if the SWA hasn't got one
and if one is needed at all and you are not allowed to use other than green/yellow cores as an earth.

I couldn't find it in the regs but somehow I seem to remember that you are not allowed to tape up
wires with green/yellow and use it as earth (although I might be wrong)

Can anyone help me with that? It looks like a bodge job to me.

Thanks guys.
 
You can use any colour you like provided they are suitably identified as to what purpose they serve.

Havent got my regs with me at the mo, but im sure someone will be able to give the number.

:)
 
To the best of my knowledge you can designate a conductor as a cpc (usually the grey) and all is well. You cannot however use a green/ yellow (or unsleved) as anything other than a cpc though since that is a specific designated use.

Also below a certian size the armout on a SWA can be used as the cpc so a 2 core would be fine.
 
I seem to recall somewhere that there is a standard for sleeving 3 phase SWA for single phase to avoid black being used as a neutral conductor:
Brown- left as it is
Black- sleeved Green/Yellow
Grey- Sleeved blue
May have even been the NICEIC but could be wrong.
 
Dont forget for the swa to comply if used as earth as well there should be bonding link (fly lead) from the earth ring to the earth block and as for the cores been utilised as earth i agree with the above as long as its correctly marked along its full exposed length.
 

Reply to any conductor as protective earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
667
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

That makes sense. Thanks James.
Replies
4
Views
86
  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top