just had quick look at ccu 12 way 100a/30ma hager isolator, problem seems to be that the rcd/isolator trips when all mcbs are on and when its wet, now turn off any two or three mcbs and the problem stops could under stand if one of the mcbs solved the problem but seems you can turn of any and it has to be two or more have done no testing as yet as it really was a quick look was thinking of neutral to earth fault but then it would still trip all the time ,faulty rcd any help would be great large house so could be in for the long hall if no ideas
 
just had quick look at ccu 12 way 100a/30ma hager isolator, problem seems to be that the rcd/isolator trips when all mcbs are on and when its wet, now turn off any two or three mcbs and the problem stops could under stand if one of the mcbs solved the problem but seems you can turn of any and it has to be two or more have done no testing as yet as it really was a quick look was thinking of neutral to earth fault but then it would still trip all the time ,faulty rcd any help would be great large house so could be in for the long hall if no ideas


Could be a loose main neutral or a neutral earth fault at the RCD or mains position, in both cases the inbalance would get worse as load is increased so turning off load regardless of order would stop the inbalance, cant undestand the wet though unless its an overheads service
 
Without any tests eveything is guesswork

The first thing I would do is eliminate the chances of 1 or more loads causing the problem
The installation tripping when its wet suggests external problems

There may be an outside light or such that is the sole cause or it may be low when wet and coupled with appliance leakage or other circuit leajkage,it is enough to tip it over

Turning off an mcb wont isolate a faulty circuit,it will eliminate load paths that may be contributing

With a neutral earth fault on the system,the load on the problem circuit may not in itself be enough to trip the rcd,but may do so with the load of a good circuit making the fault show up

As I say without testing all guess work
 

Reply to any help would be great in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
316
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
964

Similar threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
498
  • Question
Hi I've nearly completed the 2357 NVQ. I'm just a bit stuck with Permits to work, Planned program of work and method statements. I work in the...
Replies
0
Views
482

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top