Been advised its OK for 250v insulation test on eicr but not sure
The origin of the 250V test is basically so that you don't accidentally fry any equipment that may still be in circuit. So any circuit identified as 'vulnerable to testing' is where you would use a 250V setting - such as a modern lighting circuit with LED lamps or fire alarm supplies are also another.

That said, the testing regime in GN3 says to remove all appliances and lamps from circuits prior to testing so it would only apply to a situation where you can't do that due to an access issue or some other limitiation (eg, needs removal of otherwise fixed wiring). So the preference is always for a 500V test where possible, however given the lowest insulation values allowed for both settings are very low, then I would argue that if you're having to rely on a 250V test to achieve compliance then you're clutcing at straws with something that really does need investigating properly.
 

Reply to the thread, titled "Any ideas on testing eicr insulation voltages." which is posted in The Welcome Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top