Any ideas on this - old installation (3036's) on a tn-s . When the new DP isolator is switched off there is still more than 40mA in the main earth wire going from the casing of the supply to the earth bar in the CU. And there is more than 40mA difference between the line and neutral when the CU is on.
Is this an induced current from the supply cable ? Would it have implications for replacing the CU with a double rcd unit. (Thought i would put an rcd in front of the CU temporarily just as an experiment)
I have no reason to doubt the accuracy of the earth leakage clampmeter which is accurate in other situations and has the facility to just measure in the 50-60Hz band
The supply transformer is less than 100M from the house with less than 30 houses in the street. The voltage is quite high at about 245V.
Is this an induced current from the supply cable ? Would it have implications for replacing the CU with a double rcd unit. (Thought i would put an rcd in front of the CU temporarily just as an experiment)
I have no reason to doubt the accuracy of the earth leakage clampmeter which is accurate in other situations and has the facility to just measure in the 50-60Hz band
The supply transformer is less than 100M from the house with less than 30 houses in the street. The voltage is quite high at about 245V.