Hello,
220V 3P+E SUPPLY.
POLYCARBONATE PANEL
63A TP ROTARY ISOLATOR
4x 16A 220V 2P+E SOCKETS.
PROTECTED BY INDIVIDUAL 16A 30MA 2P 'C' TYPE RCBO'S.
SOCKETS WIRED USING 2 LINES PER SOCKET SO (L1-L2) (L2-L3) (L1-L3) (L1-L2).
I've looked at protecting the sockets with 2P ABB RCBO'S which offer overload protection in both poles.
The issue is they are expensive compared to standard L+N RCBO'S.
I'm thinking of using an incoming RCD and protecting each socket with a DP mcb to cut costs.
Just wondered if any of you more experienced spark's out there have any suggestions on the best and most cost effective way to protect this system?
Also with regards to RCD testing, as there isn't a neutral present and I've got 110v between phase and earth, I think I may have issues taking readings?
Again any suggestions or advice would be much appreciated.