sythai
Have a domestic customer that has part of a ring supplying a study area.
An he wants to have this extended in dado to include an additional 10-15 double sockets. To be used for computers, printers, mointers etc.
But he would like to be able to isolate these extra sockets at one point, a 'last man out switch' sort of thing.
Simples if this was a dedicated ring but it covers another room that will need to stay on.
Cant run any extra circuits/ legs in as he dosent want any floors up etc....
Only way I can think of doing this is by installing 2/3 x switched fused spurs each one supplying 5 x sockets ?
Or maybe is there a way I can make up some sort of contactor unit...?
Any thoughts please or better solutions ?
Many thanks,
Sy
Thanks Greg..... does look like a good product, bet its pretty pricey ££
After all that the customer is going to stick with no seperate isolation, makes my job a bit easier..
Thank you for all your feedback,
Sy
So would I be right then thinking I may be able to do it like this....
45a DP isolator, ring in and out on feed side, then off load side run a 4mm radial ?
You would then be spurring ALL the additional sockets from one point of the ring circuit thereby massively overloading the ring circuit at this one point....a big no no IMO.
i agree lenny, isnt this exactly what would be happening if you ran a mainline track off of the ring ??? ie, the mainline track would be a spur upon which the customer could put as many points as he wants, no no no!!!!
The ring shouldn't be overloaded (as obviously on 32A MCB), but it isn't something I would feel comfortable doing as it's not a ring nor a radial, it would just make a mess of the existing installation, and you would have to add an extra sheet to the cert saying what you had done.
What is going to be plugged in? surely a little office in someones house doesn't require much power.
no power atall. the op wants a way of extending the ring but only isolating the office which would be on that ring
Hmmm are we going away from the rule book here? hard wiring unprotected contactors and radials into a ring main, a D/P switch fuse, tripped at 20 off both legs, coming out with 4s for your radial would be a better option, why use a contactor at all? or keep to your original idea with your three spurs nothing wrong with that.
How about breaking into the ring, taking a spur to a Switched fused spur (RCD or not as the install needs). From the spur run a 2.5mm radial to feed your sockets. This is compliant even though you are in effect spurring from a spur etc, but you have protected your circuit from overload because your fused spur is limiting your new leg to 13a. Not an Ideal solution i know, but will get you out of a corner. If you do take this option, make sure your Zs is in spec at last point of the circuit extension. You would be in effect making a long extension lead.
Cheers.........Howard
sythai
Devon, United Kingdom
Any thoughts on this....
Australia
sythai,
SirKit Breaker,