Evening all...


Customer has flickering lights and seems to get worst when airsource heat pump is fired up.

Have checked all connnections are tight, tails etc, all ok ?

Could it be the incoming supply maybe, it's at the end of the line and overhead or am I missing something ?

Sy
 
Last edited:
Well those heat pumps use a lot of juice, and as you are at the end of line, volt drop may be an issue.

Have you measured the voltage at the light fittings when the pump is running???
 
had similar problem with a client. fluorescent lights in his offices were flickering. turned out he was running on 205 volts. only solution was a new supply from new tranny at nearest pole. cost him a bomb
 
Hi sythai,
Have you checked the fuse at the head?......I've had a few of these where the fuse/contacts overheat and discolours and softens the contacts.....bad contact and inconsistent supply the result.It would be apparent under load as the fuse holder will get noticably warm.....apologies if this is in egg sucking territory.
 
Hi sythai,
Have you checked the fuse at the head?......I've had a few of these where the fuse/contacts overheat and discolours and softens the contacts.....bad contact and inconsistent supply the result.It would be apparent under load as the fuse holder will get noticably warm.....apologies if this is in egg sucking territory.


ah- over here that's part of the supply
 
Saw this a while back (had been happening for months)...turned out to be a loose neutral connection on the supply into the meter or a Henley (I wasn't there to see exactly what). DNO call out, free of charge fix.
 
Can imagine they will try and deny all knowledge..... :(

Henleys, tails all good and tight that was my first thought loose neutral. Main fuse looked in good nick and wasn't getting warm, but might consider swapping for a new one which my kind friend at the DNO has given a few of (luckily someone has already cut the seals)
 
Flickering ended up full on disco lights in the end..... and then supply died!

Got DNO out and was neutral fault somewhere down the line.

I can stop worrying now, thanks for all you help,

Sy
 
on my problem, they put in a new supply cost £15000 yes 15K, and the customer dug the trench from the pole himself!
 
Chris.... yes eventually found out yesterday that couple of people down the lane also had probs. Wish I'd known this on Thursday evening before my 1.5 hour round trip through rush hour traffic, stress !! I just couldnt leave it, regular customer with young baby, right out in the sticks etc..... and I didnt get paid/charge for it, thats customer service for you :)
 
At the end of the day I would of still billed them.
I had a similar problem. What I did was made up a temp socket wired straight into supply. Put megger on volts setting in one socket and plugged kettle into other socket. Volts dropped big time.

DNO supply fault in the road.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

sythai

Arms
-
Joined
Location
Devon, United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Any thoughts please.... flickering supply
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
22
Unsolved
--

Advert

Thread statistics

Created
sythai,
Last reply from
hopkins85,
Replies
22
Views
2,970

Advert

Back
Top