Discuss Anybody know ? in the Australia area at ElectriciansForums.net
Well I never paid much attention to it after I saw that there was no earths connected to it.
Well I never paid much attention to it after I saw that there was no earths connected to it.
Well Lenny I think you should get the 10 points. I was going down the lines of the above bad boy and thinknig it was a voltage operated unit, and thought that the OP was thinking 100ma rather than 500mA and so a Typo
But your right the current operated ELCB never needed an earth connection as it worked like the modern RCD on LINE/NEUTRAL inbalance.
The old voltage ELCB needed an earth connection to it as it sensed a rise in voltage on the earth conductor.
.
I dont recall ever having seen and old looking ELCB like that one, only ever VOELCB's.