kajdean

Hello all,

Im currently training to become an electrician, for my theory ive been asked this question, its taken me a while to get my head round what i think is right, could anyone tell me if im working this out right? much appreciated.


Q. A single-phase circuit is to be wired in 70 degrees pvc insulated and sheathed single core cables to BS6004 having copper conductors. The cables are to be installed in free air, horizontal, flat spaced on vertical cable tray system.

If the Ib=135A the ambient temperature 50oc and protection is provided by a BS88 device, what is the minimum current rating for the fuse and the minimum csa of cable conductors that can be used.

A.
Ib=135A
Ca=0.71 (table 4B1)
In=160A
Cg=1.00 (table 4C1
It=225.4
Ci=N/A
Iz=N/A
Cf=N/a
Mi=N/A


160
___________ =225.4 Minimum current rating for fuse=225.4
0.71x1.00



Minimum CSA of cable =25mm2 (table 4D1A, column 11)
 
from table 4D1A, for Ib =160A, i get 50mm cable, with a fuse rating of 190A. (Iz>In>Ib)
 
as i read it, your Ib is 135A but this needs to be corrected for ambient temp by 0.71 thus giving a corrected CCC of 160A. there fore your Iz of the cable needs to be > 160A. 35mm is 162A ( table 4D1A ) which is borderline so next up is 50mm @ Iz = 197A, which gives a good margin. your MCB rating needs to be below 197A so as to open before the cable os overloaded, but above 160A, so as not to open at this level of current.
 

Reply to Anyone able to help? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
123
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
260
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top