Appliance in a bathroom | on ElectriciansForums
Discuss Appliance in a bathroom in the Australia area at ElectriciansForums.net
nnw49
Oxford
Wondering if it is legitimate to install a tumble drier in a cupboard in a bathroom.
Obviously, this will mean a socket being fitted, again inside the cupboard.
The cupboard is approx 3m from the bath/shower (other side of the room)
Is this allowed? The property is a rental.
Thanks.
N.
Hard wired into an RCD FCU so there is no 230v switch to operate then I cant see a direct problem, also make sure the zs is permitted, and to go the whole hog put a lock on the cupboard or the actual FCU in a lockable box
If it has to be switched then switch it outside of 3m
You cannot install a socket within 3m of the edge of the bath / shower cubicle, however as the location is over 60cm from the bath / shower cubicle then you can wire it to a SFCU, i.e. it must be a permanently wired appliance suitable for the location. You should consider if the tumble drier is suitable for the location and will not get directly wet.
part 7 of the regs says a socket outlet has to be over 3m away from edge of zone 1 0.6m away from edge of bath so minimum 3.6m from edge of bath or shower, but like above said you could hard wire the equipment into the switched fused connection unit and aslong as is protected by rcd happy days
Whilst BS7671 does not actually prohibit the use of Class 1 fixed or stationary equipment outside of zone 2 it's not something I would encourage, Class 2 devices more readily satisfy the requirements of locations containing a bath or shower.
As most tumble driers are Class 1 stationary equipment, if it's located 3m from zone 2 and supplied from FCU rather than a socket-outlet on an RCD protected final circuit, it would be OK, but not ideal.
My main worry and concern is the unattended operation of a tumble drier located in a cupboard, although this prevents direct access to the equipment, it could increase the fire risk by reducing the airflow in/around the drier and the possibility of poor venting, leading to increased operating temperatures and also the build up and trapping of cotton lint from the clothing leading to a combustible atmosphere. There are about 1400 washing machine and tumble drier related fires in domestic premises every year so this is a real and potential risk. The landlord of a rental property contemplating such an installation might wish as part of the risk assessment and duty of care to consider the installation of a heat detector in the bathroom and an emergency switch located outside the bathroom to disconnect the supply to the appliance in the event of a fire.
Reply to Appliance in a bathroom in the Australia area at ElectriciansForums.net
At some point, all sewage pumps will fail, or need extensive maintenance. I make it quite clear that I'm not interested in either.
There is also the ongoing problems if this is a gendered changing room.... For example, 2 or 3 burly male soldiers (you said it was an officers...