I'm trying to determine the appropiate load to install a separate oven and ceramic hob (in a domestic kitchen). Obviously I will apply diversity to provide a suitably rated protective device & cable. However, I'm scratching my head on how to apply the diversity:

Is it:

1) Oven & hob total load in kw, then apply diversity = calculated load

OR

2) Apply diversity to the total load of each individually, then combine to calculate load

The OSG (table A2) refers to 10a + 30% fl of connected cooking appliances. So am I right in thinking it's 1?
 
Yes I agree with Tel too!!

Alternatively you can check the manuf instructions. They sometimes contain the loading with diversity applied --- job done for you!
 
Thanks chaps for the quick responce, I can get on with my quote now!

Manufacturer only gives total load for each appliance (4.2+6.7kw respectively), but does specify connecting each appliance with 3c 2.5.
 
Re: Applying Diversity to separate Oven & Hob

yep.good old 6mm on a 32A MCB. good for that little load.

- - - Updated - - -

but i'd use 4mm flex on the hob, myself.
 
Manufacturer only gives total load for each appliance (4.2+6.7kw respectively) said:
Fitted a nice Kenwood (?) style all electric range cooker at the week-end and the instructions had kindly given the load with diversity applied and the cable to be used to connect with ....... cant beat following manuf instructions!
 

Reply to Applying Diversity to separate Oven & Hob in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
429

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top