I'm going to be wiring an extension(3 floors) to a retail unit which will need a new supply as the demand is quite high already(high 80's on all phases through the day).

Anyway I've totaled up the loads for each floor into Lighting and Power and Storage Heating but I'm not too sure how to apply the diversity to it, can anyone help?

Cheers
 
100% of the lighting
100% of the next largest load (probably the storage heaters?)
40% of everything else

Is how I would do it I think!
 
Just checked the On-site Guide and found this:

Lighting - 90% of total current demand
Heating - 100% of largest appliance & 75% of the rest.
Power - 100% of largest point 70% of every other point.

Lighting - I take it that means add all my lighting points up and take away 10% to give total.

Heating - Straight forward.

Power - Do I count up the number of Ring Mains and use the first Ring at 100% and the others at 70%?

If I do that I end up with this:

Lighting - 6400w to 5760w

Heating - 27200w to 21760w

Power - 11 Rings at 32A = 61440w

What do you think, does that look anywhere correct?

Cheers
 

Reply to Applying diversity? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There's a church in a town near me that has solved the heating problem for most days by building what is essentially a large timber and glass...
2
Replies
27
Views
2K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
677

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top