hi guys

ive got myself a little confused here when trying to calculate a max demand figure for the installation below.

60amp TNCS supply to a bungalow.

1x 30A Ring Main
1x 30A cooker unit(with socket)
1x 40A Shower (8.5kw)
2x 20A Radials
1x 5A Lights (7x100w)

using table 1B app 1 OSG

ring main (30a) no diversity = 30A
cooker unit(30a) 10A+30%(fl)+5A =24A
shower(40a) no diversity = 36.9A
radial(20a) 40% = 8A
radial(20a) 40% = 8A
lights 66% =3.04A

using these figures it comes out at a diversified current of 109.9Amps what am i forgeting as this cant be right can it? do i have to apply diversity to the diversified currents

when i use my usual method of adding up the MCB's and then multiplying by 0.4

40+30+30+20+20+5 x 0.4 = 58 Amps

which is what id expect. any help would be appreciated.
 
Ian the 0.4 is exactly the method I use and was shown to me by a DNO engineer many years ago as a good rule of thumb, and something I always use as that a rule of thumb, so IMO mate that looks just about right.

The thing is the shower. Quite right the OSG do have the take that it is a fixed load, and so no diversity, I always felt that was the right way to think when you look at it as a final circuit, but not in an installation as a whole.

As said before the OSG is a good guide, but it is just that, and even this tells us in the section on diversity that there are many ways to treat the subject, and eventually the amount of diversity done is purely down to the designer and experience.
 
thanks Malcom

i usually times the total of the breakers by 0.4 (rule of thumb) for max demand.
when using the OSG table 1B to work out diversified currents would this total figure then be multiplied by 0.4 ? if this is correct then it makes sense.
 
on a similar note ive noticed that the OSG states that "the C.U should be of a sufficent rating to take the total load connected to them with out the application of any diversity".

so in the case above the total load connected would be 125Amps if no diversity applied. i find this very confusing and hard to understand. help pls lol
 
on a similar note ive noticed that the OSG states that "the C.U should be of a sufficent rating to take the total load connected to them with out the application of any diversity".

so in the case above the total load connected would be 125Amps if no diversity applied. i find this very confusing and hard to understand. help pls lol


What current rating is the unit?
 
[ElectriciansForums.net] applying diversity just somthing in one of my books
 

Reply to applying diversity in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top