Just in the process of applying for a new supply from the electricity board which is a completely new one for me. Just got to the part about required KVA and that's where I'm stumbling. We're applying for a 3P supply for a domestic property. Currently I've worked out the maximum demand at 215A without the garden supplies (including a swimming pool) or the gym (25A 3P sunbed, 32A 1P steam room and 2x 16A 1P aircon units) so I'm certain that a 100A 3P supply is what we'll be needing. Based on the following calculation:
(100A x 415V x 1.732)/1000=71.878KVA
would it be safe to assume that putting down a 72KVA supply on the form would be a sensible idea. Also on the tick sheet about loads that would create harmonic distortion would it be safe to assume that I can neglect telling the supplier about the heat pumps as they will all be soft start units and shouldn't create any issues.
Thanks in advance.
(100A x 415V x 1.732)/1000=71.878KVA
would it be safe to assume that putting down a 72KVA supply on the form would be a sensible idea. Also on the tick sheet about loads that would create harmonic distortion would it be safe to assume that I can neglect telling the supplier about the heat pumps as they will all be soft start units and shouldn't create any issues.
Thanks in advance.