A

Araman

Last week I was asked to replace 4 fluorescent lamps on two circuits. The job went very smoothly and the first two were fitted and working in no time. The second two followed suit but by the time I was finished and ready to go the first two had stopped working, and nothing I do will get them working. I have, of course, checked my wiring and, to cut a long story very short, I can find 247 volts at the switch but only 128 volts at the lamp only 2.5 metres away and they will not come on. Anyone out there experienced this?
 
If you've wired them loop-through fashion, you might want to check that you've not accidentally wired them in series from the switch wire instead of the loop.

You need to expand on how you've wired them up.
 
I did not re-wire them, simply replaced the lamps. Previous electrician has not followed protocol of wiring colours and there are plenty of black live cables. Black/red at the switch which gives 247 volts. All connections are tight and L/N at lamp gives 128 volts.
 
OK, well the black - red at the switch is the switch live, which correctly reads the loop voltage. Half that same voltage at the lamps does tend to suggest to me that the switch live has been mixed up with the loop live out to the fixtures. Or as Malcolm said, you've got a loose connection to the lamp.

Are they wired on three way plates (like a ceiling rose), by any chance?
 
No ceiling rose. The cables simply protrude from the plaster direct into the 5ft fluorescent. I have checked all wiring I can see but now it seems I have to start lifting floorboards to find the fault, which, naturally I am loath to do, but I have checked all connections several times and nothing is loose. Many thanks to all who offered advice.
 

Reply to Araman in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

Shhh, don't tell the Chinese they want a bit of the action.
Replies
1
Views
591
I'm not sure on the environmental implications, a good quality integrated fitting will last many years and be more energy efficient than the GU10...
    • Like
Replies
13
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top