I wouldn't have said condensation alone would cause an arc like that. Especially in an LV board.
i thought that at first, when you look at the Mcb those prongs have a plastic cover over them and these were still in place apart from the centre cover had come loose after the fault along with the fact it being the second way down makes it even stranger.I would have maybe said something loose inside the panel, finally moved due to vibration or similar. You'll struggle to melt copper like that without a direct short.
Hi, there was nothing that could of shorted at all, clipped in nice and tight, only one of the covers had come loose and the others were still intact and secure, the busbars on the gear tray were still nice and cleanAs all the burning appears to be down the middle was there anything that could of shorted between the front and the terminals?
looks an expensive repair and once done it might just do it again
there is some rust showing on the cabinet
I would have maybe said something loose inside the panel, finally moved due to vibration or similar. You'll struggle to melt copper like that without a direct short.
Ah, didn't see the second set of pics with the rust, that's the problem with reading the forum over a slow mobile phone connection. But the SWA's are deffo in the top of the board, or the cable basket's on the floor open side down!
Difficult to judge,just from pictures,but looks like moisture has been introduced directly to MCB's,possibly through a single conductor. Capillary action is stronger than imagined,and can be assisted if there exists an atmospheric pressure differential,between one end of the conductor and the other,say negative pressure in plant room as a result of ventilation,or a positive pressure + moisture,at its' termination. If you were as sad as i am,this can be checked using an inclined manometer and a pipe the length of the longest circuit...or visually...or just move on with your life,peg...:smilewinkgrin:Had a fault like that once, perplexing. Turned out to a split shroud on a SWA supplying an A/C unit outside on the roof, the water was getting in and making it's way down through the armoring and core gaps into the panel, Took some finding luckily I was called back to it when it was raining, worth a look. Good luck.
I stand corrected not sure why I thought they were in at the bottom ... but the gland termination would be good place to spot that as it would be all corroded too and Im sure the OP would have spotted it when looking for leaks.
Yes it is in a hot plant room, there is some passive ventilation system which i dont really know much about, when we changed the DB we advised the client to check with the installer of the ventilation system, there is a large slatted grill in the plant room wall opposite this DB but about 4 metres away