Harry Worth
Sorry folks if this topic is done to death. I've just been working with a spark who's put 16mm tails on a 100A fuse. I queried this and he responded with 'I'll show you in the regs - It's OK'. I've since tried to find the relevant table. Looking at table 4D1A - it gives 87A current carrying capacity for single core 70 degree thermoplastic clipped direct. Is this the correct table? The table doesn't show values for cables spaced or in free air. The tails in this instance are separated, short and not directly clipped to wall at some points. My question - does this mean the actual capacity can be taken as higher than 87A as the conditions are better than those in this table? If i take the 25mm table the capacity increases from 114A (ref method C) to 130A for spaced by 1 diameter. If I apply this factor to 16mm cable it suggests the cable is good for 99A (appreciate the calc's a bit rough and ready - I've probably ignored a square law). The house doesn't have an electric shower etc so current peaks are probably well within the 87A in any event.