H

Harry Worth

Sorry folks if this topic is done to death. I've just been working with a spark who's put 16mm tails on a 100A fuse. I queried this and he responded with 'I'll show you in the regs - It's OK'. I've since tried to find the relevant table. Looking at table 4D1A - it gives 87A current carrying capacity for single core 70 degree thermoplastic clipped direct. Is this the correct table? The table doesn't show values for cables spaced or in free air. The tails in this instance are separated, short and not directly clipped to wall at some points. My question - does this mean the actual capacity can be taken as higher than 87A as the conditions are better than those in this table? If i take the 25mm table the capacity increases from 114A (ref method C) to 130A for spaced by 1 diameter. If I apply this factor to 16mm cable it suggests the cable is good for 99A (appreciate the calc's a bit rough and ready - I've probably ignored a square law). The house doesn't have an electric shower etc so current peaks are probably well within the 87A in any event.
 
Sorry Harry I thought you meant your total load is 87A. If the total load after diversity is below this then right now you'd be ok with 16mm tails, but (it's a big but) what's to say that next week they're not going to go out and buy a megawatt shower?
I'd stick 25s in as a matter of course but that's just me:)
 
There must be many, many houses out there with 16mm tails and 100a main fuse. It's not ideal, and I'd replace with 25mm if it's convenient to do so, but as Murdoch says, it's nothing to fret about. I certainly wouldn't go breaking seals etc. In the case the OP is on about, I'd have installed 25mm no question.
 
think he meant instantaneous shower. anyway, i posted some time ago where a pub kitchen was pulling 90+A through 16mm and i measured the cable temp. after 45mins. ( that's when the 63A breaker tripped) and it had just got to 39deg., well short of the max. 70deg. so i also would not lose any sleep over it. obviously, from a design stage, you'd fit 25mm.
 
think he meant instantaneous shower. anyway, i posted some time ago where a pub kitchen was pulling 90+A through 16mm and i measured the cable temp. after 45mins. ( that's when the 63A breaker tripped) and it had just got to 39deg., well short of the max. 70deg. so i also would not lose any sleep over it. obviously, from a design stage, you'd fit 25mm.

I do too ..... I was just being a pedantic sod ;)
 
What size are the cables from the main fuse to the feed side of the meter? Are they 16mm? If so changing the load side tails only upgrades part of the installation,albeit the feed tails are the DNOs baby.
I worked for a DNO for a long time,and after fitting 16mm tails off an 100a main fuse since time began,one day it dawned on someone 16mm was rated about 97a so we then started fusing down to 80a.
I would fit 25mm as someone else has said, but I wouldn't lose a great deal of sleep over this either way.
Just a thought-have you actually checked the size on the fuse itself? It may say 100a on the carrier but it may be an 80a inside?
 

Reply to Are 16 mm meter tails good for 99A? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
281
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
791

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
803
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top