My ex-Next-Door-Neighbour has asked me about changing a shower at his new house.
Now I can't do it, (I'm not a scheme member) as it's not a like for like, he wants an uprated one.
But I told him previously he would be looking at replacing the 6mmsq Twin+cpc with 10mmsq if he wanted to uprate because the existing is only just compliant.
He rang someone out of the local paper and they said the 6mmsq is perfectly adequate.
I think not, please could someone check my calculation and reasoning:
MCB is 40A, RCD protection provided (16th Ed style board)
Firstly, it's not a recognised combination in table 7.1 of OSG.
But calculating each element separately:
Existing shower is 240V 8.5kW, 230V 7.8kW.
Supply voltage at the new house is 230V so that's 33.91A
Between CU and loft, cable run is a mix of buried in plaster and enclosed in trunking.
So, Reference method B brings that down to 38A. (Why no mention of B in OSG?)
In the loft, the cable runs over the top of the insulation to the pull switch, then is clipped to the side of the joists over to the shower.
That's reference method 100 which brings it down again to 34A.
And the 40A breaker is OK because of 433.3.1 (ii)
So I can demonstrate that the existing arrangement is compliant (Just!) but there's no way a shower of higher rating should be fitted to this circuit.
They trust my engineering judgement so will not use that guy out of the paper...
They said they take quite a few mins in the shower and they're all in there one after the other so don't want something overheating.
And as they've just decorated everywhere except the bathroom, I've discussed a few options and it looks like the solution will be to fit a thermostatic mixer shower - far more powerful and no part P nonsense.
Simon.
Now I can't do it, (I'm not a scheme member) as it's not a like for like, he wants an uprated one.
But I told him previously he would be looking at replacing the 6mmsq Twin+cpc with 10mmsq if he wanted to uprate because the existing is only just compliant.
He rang someone out of the local paper and they said the 6mmsq is perfectly adequate.
I think not, please could someone check my calculation and reasoning:
MCB is 40A, RCD protection provided (16th Ed style board)
Firstly, it's not a recognised combination in table 7.1 of OSG.
But calculating each element separately:
Existing shower is 240V 8.5kW, 230V 7.8kW.
Supply voltage at the new house is 230V so that's 33.91A
Between CU and loft, cable run is a mix of buried in plaster and enclosed in trunking.
So, Reference method B brings that down to 38A. (Why no mention of B in OSG?)
In the loft, the cable runs over the top of the insulation to the pull switch, then is clipped to the side of the joists over to the shower.
That's reference method 100 which brings it down again to 34A.
And the 40A breaker is OK because of 433.3.1 (ii)
So I can demonstrate that the existing arrangement is compliant (Just!) but there's no way a shower of higher rating should be fitted to this circuit.
They trust my engineering judgement so will not use that guy out of the paper...
They said they take quite a few mins in the shower and they're all in there one after the other so don't want something overheating.
And as they've just decorated everywhere except the bathroom, I've discussed a few options and it looks like the solution will be to fit a thermostatic mixer shower - far more powerful and no part P nonsense.
Simon.