So there’s a hotpoint oven hae60ks....
The manual states its10.7 kw....divided that by 240 is 45amps.
The manual also states is must be installed with a 6mm cable connected to a 32amp breaker.
Some people online are saying a 6mm cable is max rated at 32amp
But i read that clipped direct it’s max rated to 47
So my basic question is... I have a 6mm cable running up 2 meters stud wall, above the ceiling for 12meters no insulation and then 2 meters down another stud. It’s currently on a 32amp breaker.
Is this going to be sufficient enough? With diversity taken in to account it’s doable. But my missus cooks 3 different meals everyday for dinner.
I also read that a Type B 32amp breaker won’t trip out untill about 3-5 times it’s rating which is what? 90amps?