Ramjam - are you sure that the internal RCMU (residual current monitoring unit) fitted to the TL range of SMA inverters is a Type B RCD? Or are you referring to an additional device fitted internally? Do you interpret this to mean that even a Type A RCD is not required?

I'll stick my neck out here with my below comments/queries as I want to understand better but I'm simply not qualified to interpret the regulations well enough but have tried to form a simple understanding myself, I'll apologise in advance and stand corrected on anything that I've got wrong:

Why "this is fine in Germany but not in the UK" for 100mA trip limits? Surely a necessity for a 30mA trip limit (for "human" protection") should be avoided by virtue of the fact that the PV installation incorporates Class II equipment and contains non-pluggable (into sockets) devices. If other factors (fire risk, cable type/routing etc) dictate that an RCD should be used then doesn't the fact that the DTI guidelines state that the AC supply from the inverter to the DB/CU should be unique to the PV system and not have any other devices or circuits connected to it, mean that a 100mA trip limit (or more) is perfectly acceptable as it's related to a separate part of the household/property circuit from a supply/load point of view?

Bonding the array - the DTI guide suggests that whenever a TL inverter is being used, you must bond the array in some form or fashion (earth spike or direct to CU earth terminal). Does the DC leakage current you mention above from the array have any relation to DC leakage currents generated by the inverter itself? Are they the same thing? Having a TL inverter anyway means that there is no simple separation between the DC and AC sides. Hence an RCD capable of protecting against DC leakage faults/currents (pulsed or pure) as well as the fundamental protection against AC ground/leakage faults is required as a minimum. This means that either a Type A or a Type B should be selected. Type AC devices are used in the UK still but are not capable of providing protection if the internal coil is saturated with a DC leakage current. I believe that half the recent confusion with the current SMA statement(s) are that, in Germany, they don't use Type AC RCDs at all, even for their standard domestic electrical circuits. Their "base unit" if you like is the Type A. So, when they say "you don't need a Type B" the fact that they omit any mention of a Type A device is simply because that is the defacto RCD in use over there anyway so doesn't need to be clarified.

I am curious as to people's interpretations of SMA's (and Fronius', and PowerOne's) documents and whether anyone has actually spoken to SMA, or others, directly about this. It still seems like a bit of a grey area to me. I do know that discussions are still ongoing over in Germany and that the UK regulatory bodies are involved in trying to clarify the exact requirements. That's what I am told anyway.

My next area to investigate is surge/lightning protection........we're talking to Dehn now about their products.

Andy (off to don flameproof suit)
 
I may be missing something important here, but why are RCDs being fitted anyway, assuming that the cable route doesn't call for it?
 
Reg 551.7.2 (iii) might be the reason people are fitting RCD protection and 30mA.

They would be wrong to do that though because that regulation is talking about generating sets in general. The specific rules for PV in 712 do not allow a PV generator to be connected to the load side of the protective devices of a final circuit. It has to be on its own mcb in order that it is connected to the supply side of the protective devices for final circuits of the installation.

Regards
Bruce
 
Section 551.7 for Additional Requirements (note that ) for Installations where the generating set (PV ARRAY) may operate in Parallel with other sources including systems for distribution of electricity to the public ..........and reg 551.7.2 is upheld by reg 712.411.3.2.1.1. But some might be looking at the reg as a whole.

Regs 551.7.4, 551.7.5 and 551.7.6 all refer us to BS 50438 [h=2]
Requirements for the connection of micro-generators in parallel with public low-voltage distribution networks
[/h]Status : Current Published : January 2008


So I would have thought that this section would be relevant.
 
I do not think so. 551.7.2 has 2 cases: generator on the supply side and generator on the load side. With PV, the generator has to be on the supply side from 712.411.3.2.1.1, so all the load side conditions are irrelevant because the generator should not be connected in that way. Short answer only as I am away now for the day - I'll see where this has gone later.
Regards
Bruce
 
Section 551.7 for Additional Requirements (note that ) for Installations where the generating set (PV ARRAY) may operate in Parallel with other sources including systems for distribution of electricity to the public ..........and reg 551.7.2 is upheld by reg 712.411.3.2.1.1. But some might be looking at the reg as a whole.

Regs 551.7.4, 551.7.5 and 551.7.6 all refer us to BS 50438 [h=2]
Requirements for the connection of micro-generators in parallel with public low-voltage distribution networks
[/h]Status : Current Published : January 2008


So I would have thought that this section would be relevant.

You have to remember the Regs are a minimum standard and yes your right there is no need to if the installation is fitted on the supply side to fit an RCD, but some may take the reg as an whole and fit an RCD.

Same as there is no regulation that makes me fit a double pole RCBO in a TT system if the DB I was fitting it to had a double pole 100amp main switch, but I feel IMO that the regs does not go far enough and so I fit double pole protection devices for TT.
 
Dear all,

Just to come back to the subject of RCD type selection, I have asked Doepke UK (who are currently in Germany discussing the whole TL inverter situation) to provide me with a generic guide to RCD type selection when fitting TL inverters with built-in RCMUs (Residual Current Monitoring Units). As I hinted at in my previous post above, an RCMU is not the same as a Type B RCD. Anyway, hopefully the below will help to clarify things somewhat. I'm assuming that those reading this will understand the differences between Type AC, Type A and Type B RCDs, as well as the effect that DC currents (pulsed or pure) will have on the trip coil inside an RCD protective device (saturation causing failure of coil to energise/release etc).

From Doepke UK:

The Installer needs to verify from the inverter manufacturer the inherent d.c. leakage current in normal operation ( i.e. the RCMU will have a minimum d.c operating current – this is normally around 15mA d.c.)
If the Installer can guarantee that there will be no d.c. leakage current ( today – this requires an isolating transformer ) he can use a Type-AC RCD.

If using a TL inverter, and the inherent leakage current is less than 6mA d.c. the installer can then use a Type-A RCD ( Doepke are not aware of any TL PV inverters where the RCMU will limit the leakage current to 6mA or less)

If the TL inverter's leakage current is more than 6mA d.c. (Doepke cannot guarantee the operation of the Type-A RCD under the existing standards), the installer will then need a Type-B RCD.

The customer is responsible for the PV installation – not the inverter manufacturer

So, this is where our concerns stem from. On the one hand the RCD manufacturer is reinforcing the DTI guideline but on the other hand the TL inverter manufacturer (for example, SMA) are stating in their documentation that a Type-B is not required and a Type-A is adequate. At the end of the day, if installers are happy to defer to SMA's current documentation then that's perfectly fine, just fit Type-A units. Where doubt exists, or the manufacturer cannot clarify, then perhaps it is better to err on the side of caution and fit a Type-B.

(Don't shoot the messenger....just trying to share info)
 
Dear all,

Just to come back to the subject of RCD type selection, I have asked Doepke UK (who are currently in Germany discussing the whole TL inverter situation) to provide me with a generic guide to RCD type selection when fitting TL inverters with built-in RCMUs (Residual Current Monitoring Units). As I hinted at in my previous post above, an RCMU is not the same as a Type B RCD. Anyway, hopefully the below will help to clarify things somewhat. I'm assuming that those reading this will understand the differences between Type AC, Type A and Type B RCDs, as well as the effect that DC currents (pulsed or pure) will have on the trip coil inside an RCD protective device (saturation causing failure of coil to energise/release etc).

From Doepke UK:

The Installer needs to verify from the inverter manufacturer the inherent d.c. leakage current in normal operation ( i.e. the RCMU will have a minimum d.c operating current – this is normally around 15mA d.c.)
If the Installer can guarantee that there will be no d.c. leakage current ( today – this requires an isolating transformer ) he can use a Type-AC RCD.

If using a TL inverter, and the inherent leakage current is less than 6mA d.c. the installer can then use a Type-A RCD ( Doepke are not aware of any TL PV inverters where the RCMU will limit the leakage current to 6mA or less)

If the TL inverter's leakage current is more than 6mA d.c. (Doepke cannot guarantee the operation of the Type-A RCD under the existing standards), the installer will then need a Type-B RCD.

The customer is responsible for the PV installation – not the inverter manufacturer

So, this is where our concerns stem from. On the one hand the RCD manufacturer is reinforcing the DTI guideline but on the other hand the TL inverter manufacturer (for example, SMA) are stating in their documentation that a Type-B is not required and a Type-A is adequate. At the end of the day, if installers are happy to defer to SMA's current documentation then that's perfectly fine, just fit Type-A units. Where doubt exists, or the manufacturer cannot clarify, then perhaps it is better to err on the side of caution and fit a Type-B.

(Don't shoot the messenger....just trying to share info)

Very useful piece of information Thank you.

As I noted on another thread I find it worrying that Inverters designed for the European market are not geared for UK Installation methods. I know the BS 7671-2008 denotes that manufacturers instructions must take precedent but I'm concerned that sometimes these instructions do not take UK standards into consideration
 
Exactly Malcolm, I think your concerns are quite valid to be honest. This is why I mentioned before about Germany not using Type AC RCDs anymore and potential confusion with the likes of SMA not clarifying that Type A RCDs are acceptable (not on all their documents relating to this anyway). Hopefully the ongoing discussions within the industry will eventually lead to further clarification...
 
Is this not a fault of the MCS product accreditation process. Surely if these devices attain such certification then the whole installation process should be reviewed as part of signing the product off, otherwise you have an MCS certified product conflicting with BS7671 or at the very least clouding the decision process on protection and bonding.

Ive had a look at the MCS cert for the SMA 4000TL and the max permisable DC injection is 20mA with the cert denoting a max pass through result of <14mA
 
I am Confused, I get the point that you dont need to earth the array if you have a seperation transformer in the inverter but if you installed a inverter such as a Sunnyboy HF which has no transformer you have bond the array to the main earth or earth rod if pme.

But why would you carry out a bond if you think about the array is out of any earth zone and out of reach. Most panels are double insulated to me you are only creating problems when lighting strikes and if you use a earth rod all you are doing is creating a earth on the roof which is out of reach.
 
Er the HF inverter is High Frequency and does have a transformer so no earthing is required for HF inverters, only TL on PME systems.

Second para, I agree but the DTI solar install tree states the array must be earthed.
 

Reply to array earthing / bonding in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
Replies
11
Views
1K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top