M
Matt_M
After our recent NICEIC inspection, we were advised to earth ALL arrays by the inspector.
This is apparently common practice in other countries due to the chance of capacative coupling causing an AC voltage to occur on the panel array.
Due to the various safety features used in inverters, we were a little sceptical about this, however, upon testing, our rig did indeed have a substantial AC touch voltage.
The inverters we were using are Soladin 600's, and we recorded a voltage of 20v AC on the array frame.
This could cause corrosion in the long term, and to prevent this we are going to be earthing all installs from now on.
I would be most interested to hear if other people are seeing the same traits. Give it a go and measure your next install.
Thanks,
Matt