As a requirement of BS7671 | on ElectriciansForums

Discuss As a requirement of BS7671 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

T

taka

Hi, As a requirement of BS7671, cables used for lighting must have a protctive conductor included within the sheaving.
Could tell me where I can find this regulation in BS7671?
I am sorry for such a basic question.
But I appreciate if somebody can help me.
Best regards,
 
There is no such requirement. BS7671 requires that all accessory points have a cpc run to them but does not prescribe the method by which this must be achieved. You could use twin with no cpc and run a seperate cpc. It'd need to be 4mm though!!! So, if you think about it, from an engineering point of view a cpc in twin sized to be large enough for any device the cable could be connected to is by far the best and most cost effective solution to the requirement.
BS7671 does quote BS6004 though - don't know the ins and outs of that standard, but I'd bet it requires a cpc. I've tried buying single with no cpc but no-one seems to do it, only single plus cpc.
 
Upvote 0
Hi, As a requirement of BS7671, cables used for lighting must have a protctive conductor included within the sheaving.
Could tell me where I can find this regulation in BS7671?
I am sorry for such a basic question.
But I appreciate if somebody can help me.
Best regards,

PC electric has answered your question, so i wont exapand.

But what i will say is, You do not need to apologise for asking a question, nor do you need to say that what you are asking is basic.

There are only 2 types of questions, those you know the answers to, and those that you dont.
There are no basic questions and there are no silly questions.

Please carry on asking, if you dont ask, you dont learn. I have been at this game for over 30 years, and i still ask, because i dont know it all yet.

Sorry for the rant, but it annoys me when people come on here and feel that they are below the others who contribute, you aren't.


Cheers............Howard
 
Upvote 0
[ElectriciansForums.net] As a requirement of BS7671Hi PC Electrics. Thank you very much for the quick reply. As you can see this is the question. I answered it correctly but I just wanted to find out it from the BS7671 to get used to it before my exam.
 
Upvote 0
Thank you very much for your advice!!!!!
Actually it was first time to posting for me.
It is great that somebody can listen to my question and reply.
:wink_smile:
 
Upvote 0
There is no such requirement. BS7671 requires that all accessory points have a cpc run to them but does not prescribe the method by which this must be achieved. You could use twin with no cpc and run a seperate cpc. It'd need to be 4mm though!!! So, if you think about it, from an engineering point of view a cpc in twin sized to be large enough for any device the cable could be connected to is by far the best and most cost effective solution to the requirement.
BS7671 does quote BS6004 though - don't know the ins and outs of that standard, but I'd bet it requires a cpc. I've tried buying single with no cpc but no-one seems to do it, only single plus cpc.
I,ve seen black double insulated singles with no cpc our local council wire all their house lighting in singles,red has cpc and black doesnt can,t remember who makes them though.
 
Upvote 0
Hi PC electric. As Sirkit Breaker agreed your reply. I will take your advise and try to study what you said. Thank you very much for your reply.
 
Upvote 0

Reply to As a requirement of BS7671 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
414
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It was a one time £19.99 fee. I'll be reaching out to them though to get that back. It was the only online extensive bank of questions that I...
Replies
7
Views
1K
  • Question
If you are using Zdb you do not add on Ze as that is already incorporated into Zdb.
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top