I have my assessment coming up for my two installations and am not sure about one of them.
I've run 16mm T&E from meter in my house to CU in extension carrying 100A Main Isolator, 63A RCCB, 32A mcb socket circuit, 50A mcb shower circuit, 6A mcb light circuit.
The main DB in the house has the usual 16mm E in MET and 10mm bond to services ( TN-C-S ).
The PFC at the extension CU is 0.70 KA or 700amps and my calc is as follows:
Sq Rt 700 x 0.1 / 115 = 2mm Earth.
But the OSG says I need 16mm E conductor.
The extraneous metal work in the extension are a continuation from main house so no bonding needed at extension CU.
Do I need to run 16mm from extension CU to MET in house as well as the 6mm E from 16mm T & E?
Thanks for any replies.