Apologies for the complexity of this question, but there’s no easy way to explain it.
This is a remote Norfolk house and workshops, developed over 30 years.
Due to diversification, building B on the plan needs more power than originally expected, and building D is a recent addition. I’d like the forum’s opinion on whether my proposed upgrade plan is a good way to go.
INSTALLATION NOTES
Buildings B and D are currently supplied as follows:
Main supply at DB1 (Main house) 3-phase x 100A, with direct feed to:
25m x 25mm (red) to DB2 (Barn), then 32A MCB to:
95m x 16mm (org) to DB4 (Store), then 20A MCB to:
96m x 10mm (yel) to DB5 (B-block), then:
Temp direct feed to 25m x 16mm (grn) via JB to DB11 (D-block). Note 10mm in, 16mm out is not a mistake: is was a temporary feed, piggy-backed off the B-block supply, awaiting later upgrade for building D.
Building F (‘Steel shed’) is supplied by a different route:
Main supply at DB1 (Main house) 3-phase x 100A, then 40A MCB to:
12m x 16mm (vio) to DB3 (Old milking parlour), then 20A MCB to:
170m x 16mm (blu) to DB6 (Steel shed)
I’m thinking of tapping into the last (blu) cable above at point X, to provide a branch to feed building D as well, via a proposed new (dashed black) 85m run of 25mm. Overall run DB3 to DB11 approx 200m of mixed 25mm and 16mm
This would have these advantages:
1. To take the load off the red > org > yellow run which is in only 10mm for the last 96m, to supply only building B, as originally intended.
2. Provide a 20A x 3 feed to the new workshop at building D, which is adequate.
3. Remove any need to dig up the formal garden area, or to get another SWA into any existing DB which is already full, or, at the house end, install difficult cable runs in the listed building. The proposed method is an easy trench across a field which can be finished in a day without mess or damage.
Of course it means that both buildings F and D will share a single 20A supply from DB3. I have no idea if this is a standard way of doing things. Technically it’s fine as both buildings are never in use at the same time, with F being only for storage, with a few lights and 13A sockets.
And what about tapping into a four-core 16mm SWA? Has anyone done this with existing cables which might be a bit tight in the ground. I’m hoping that disinterring a few meters of the existing run should give a bit of wiggle room. Plus using a bigger-than-necessary u/g resin joint should give room to work.
What do people think? Am I on the right track here?
I’m a bit stuck as I do need to work with the existing underground infrastructure, and get this done quickly.
Next year a brand new run of 35mm from the main switch to supply to B & D together will finish the job properly.
This is a remote Norfolk house and workshops, developed over 30 years.
Due to diversification, building B on the plan needs more power than originally expected, and building D is a recent addition. I’d like the forum’s opinion on whether my proposed upgrade plan is a good way to go.
INSTALLATION NOTES
- All cables are direct-buried 4- or 5-core SWA. Many were existing, with smaller CCA than ideal.
- All DBs are recent Hager three-phase boards, with local earth stakes.
- Most SP outgoing circuits are protected by RCBOs.
- There is good load balancing across phases, especially for lighting.
- When calculating volt drop note that a new pole transformer is shared between only three domestic properties, with the actual no-load voltage at this site never below 250V. I have never metered anything below 242V anywhere, even with everything on at the end of all the long runs, which never happens in normal use.
- The daisy-chaining of sub-mains to sub-mains is not ideal, but is there for historic reasons. Nuisance tripping all up the line has never happened.
- All buildings may be considered as light domestic loads. There is no heavy machinery.
- Disregard the solar panels visible on building F: these we installed by me, and feed back to inverters in the old milking parlour, by taking the DC MV outputs on new SWA runs, not shown.
Buildings B and D are currently supplied as follows:
Main supply at DB1 (Main house) 3-phase x 100A, with direct feed to:
25m x 25mm (red) to DB2 (Barn), then 32A MCB to:
95m x 16mm (org) to DB4 (Store), then 20A MCB to:
96m x 10mm (yel) to DB5 (B-block), then:
Temp direct feed to 25m x 16mm (grn) via JB to DB11 (D-block). Note 10mm in, 16mm out is not a mistake: is was a temporary feed, piggy-backed off the B-block supply, awaiting later upgrade for building D.
Building F (‘Steel shed’) is supplied by a different route:
Main supply at DB1 (Main house) 3-phase x 100A, then 40A MCB to:
12m x 16mm (vio) to DB3 (Old milking parlour), then 20A MCB to:
170m x 16mm (blu) to DB6 (Steel shed)
I’m thinking of tapping into the last (blu) cable above at point X, to provide a branch to feed building D as well, via a proposed new (dashed black) 85m run of 25mm. Overall run DB3 to DB11 approx 200m of mixed 25mm and 16mm
This would have these advantages:
1. To take the load off the red > org > yellow run which is in only 10mm for the last 96m, to supply only building B, as originally intended.
2. Provide a 20A x 3 feed to the new workshop at building D, which is adequate.
3. Remove any need to dig up the formal garden area, or to get another SWA into any existing DB which is already full, or, at the house end, install difficult cable runs in the listed building. The proposed method is an easy trench across a field which can be finished in a day without mess or damage.
Of course it means that both buildings F and D will share a single 20A supply from DB3. I have no idea if this is a standard way of doing things. Technically it’s fine as both buildings are never in use at the same time, with F being only for storage, with a few lights and 13A sockets.
And what about tapping into a four-core 16mm SWA? Has anyone done this with existing cables which might be a bit tight in the ground. I’m hoping that disinterring a few meters of the existing run should give a bit of wiggle room. Plus using a bigger-than-necessary u/g resin joint should give room to work.
What do people think? Am I on the right track here?
I’m a bit stuck as I do need to work with the existing underground infrastructure, and get this done quickly.
Next year a brand new run of 35mm from the main switch to supply to B & D together will finish the job properly.