I'd like to put 3.040kW on one tracker (16xUpsolar 190M, Vm 36.3, Im 5.23, Voc 45.1, Isc 5.55 and power tolerance +-3%) as two strings of 8 so Voc max would be 360.8 and Isc 11.1. so well within the current and voltage input limits of each tracker however the total power input would be 3040W ie over the 3kW input limit albeit only by 40W. In reality, is this going to be a problem or will the tracker just find a less optimum point on the IV curve?
PS, the string tool says no but in reality will it harm the inverter, warranty issues notwithstanding...
PS, the string tool says no but in reality will it harm the inverter, warranty issues notwithstanding...