hi all

just wondering if any of you know anything about auto power correction? the reason i am asking is i have several 100amp single phase installations that are running at full capacity, so i was wondering if power correction would reduce the full load current? therefore reducing running costs? probably 80 - 90 amps of that are motors and maybe 5 - 10 amps are fluorescent lighting which do have pf capacitors fitted as standard. if any one has any info it will be greatly appreciated as i have no real experience in this field.

regards
gary
 
How are these supplies metered?
Most 100A supplies are on KW/h meters so you wouldn't make any savings.
 
The current, voltage and power factor at the motor terminals do not change. The current and power factor between the capacitors and the supply are affected by the addition of the capacitors. The power drawn by the motor does not change. In effect, the capacitors are supplying some of the magnetising current of the motor, instead of it coming from the supply.
 
If we base the loading as purely inductive 100A @415V = 60KW @ .8PF
Adding 30KVAr of capacitors will lower the current to 87A @415V = 60KW @.95PF. It still equals 60KW that you will have to pay for.
You need to determine the loading of the motors on you system. The PF correction can not be switched in en-mass but needs to come in in stages. Otherwise you will have over correction
To be honest you should look at having your supply up rated and forget PF correction. There’s no financial gain from it with KWHr meters. If you were on KVA meters there would be.
If your thinking of lowering the line current by PF correction so you can add more load then I think your heading down a dangerous road.
 
Last edited by a moderator:
What are the ratings of capacitors needed to a)correct pf b)reduce starting current of 1ph/3ph induction motors of different hp/rpm.Can someone give a link?.Thanks
 
thanks for your replies

i thought it wouldnt be that simple, you are right upgrading supply would be the best solution, but the cost can be huge. so i was iust wondering could power correction be used.

many thanks
gary
 

Reply to automatic power correction panel in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
855

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
616
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top