I don't know why I've not noticed before but the disconnection time for final circuits greater than 32A is 5 secs on a TN earthing arrangement. Does that mean a shower has a disconnection time of 5 secs? Although this circuit would also fall under protection of an RCD??
Also, cooker circuits would fall in this as would many other designated circuits. So, this is related to ADS? So in order to meet disconnection times our circuit Zs would need to be compliant with specified limits. The Z's values listed for say a 40A type B, is that figure based on the circuit disconnecting within 5secs or 0.2secs?
Bit early for this and I'm probably over thinking this haha
Also, cooker circuits would fall in this as would many other designated circuits. So, this is related to ADS? So in order to meet disconnection times our circuit Zs would need to be compliant with specified limits. The Z's values listed for say a 40A type B, is that figure based on the circuit disconnecting within 5secs or 0.2secs?