The more compact a lamp the higher the chance of a ionized path been created as the filament blows, hence a GLS was an occasional issue but the GU10 were a nuisance, but as i said before it dosn't always do it and nearly always happens when switching the lamp on, the bright flash you sometimes see is the ionized short which is many times brighter than the lamp itself but it only lasts a fraction of a second, if the lamp glows brighter than normal for quite a duration (seconds or minutes) then the tungsten coils have tangled lowering the filament resistance thus increasing the current but as it wasn't designed for this higher current it dosn't last long as it just overheats and pops but this wont a ionized path as it a slow melt.

The type rating of and mcb is the tolerance of inrush associated with inductive loads, and due to an ionized track been a short circuit and not an inductive inrush using the time/current curve charts wont be effective but because the ionized path collapses pretty much as soon as its created you may get the occasional benefit of fitting a type 'C' instead of a 'B' because the current rise can be limited because of the speed of the decay of the short circuit. Its variable as to current flow and time so really not reliable value to afford it in the design stage although if Zs is met it wouldn't do any harm to fit a 'C', they cost the same.
 
Regardless of all the impressive technical explanations I've found changing type B's for C's where GU10's are fitted has dramatically reduced or even eliminated nuisance tripping when lamps fail.....Good enough for me.
 
Regardless of all the impressive technical explanations I've found changing type B's for C's where GU10's are fitted has dramatically reduced or even eliminated nuisance tripping when lamps fail.....Good enough for me.

quite possibly. just because we 're not sure exactly why something works, doesn't mean it don't work. it could just be that the short duration fault current is below the trip threshold of a type C.
 
Re' GU10 50watts, i stopped using them yrs ago, they are anergy hungry, high temp' running and added to this they have this nuisance tripping issue attached LED equiv's are now getting affordable and ive yet to have a customer refuse them because of the extra cost, its all about sales pitch and showing them the real benefits in the long term....

Although im having difficulty getting inrush details of LED lamps and recommended no's per type 'b' or 'c' as manufacturers haven't fully tested them to their products.
 
i don't think inrush current, if any , of a 5 or 7 watt LED is going to trip anything. unless you're using milliamp breakers.
 
Its inductive loading, agree with one or two but when you start getting several or more switching on together you'll be supprised at the combined surge it creates, im waiting on mcb manufacturers spec but they already said there will be a limit dependant on type of mcb, im pretty sure others have already posted with this very problem when having a large no' off LED's switching together and we are not talking 'silly large'
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wirral
Business Name
Farm electrics

Thread Information

Title
b type or c type
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
Farmelectrics,
Last reply from
Darkwood,
Replies
20
Views
7,454

Advert

Back
Top