The more compact a lamp the higher the chance of a ionized path been created as the filament blows, hence a GLS was an occasional issue but the GU10 were a nuisance, but as i said before it dosn't always do it and nearly always happens when switching the lamp on, the bright flash you sometimes see is the ionized short which is many times brighter than the lamp itself but it only lasts a fraction of a second, if the lamp glows brighter than normal for quite a duration (seconds or minutes) then the tungsten coils have tangled lowering the filament resistance thus increasing the current but as it wasn't designed for this higher current it dosn't last long as it just overheats and pops but this wont a ionized path as it a slow melt.

The type rating of and mcb is the tolerance of inrush associated with inductive loads, and due to an ionized track been a short circuit and not an inductive inrush using the time/current curve charts wont be effective but because the ionized path collapses pretty much as soon as its created you may get the occasional benefit of fitting a type 'C' instead of a 'B' because the current rise can be limited because of the speed of the decay of the short circuit. Its variable as to current flow and time so really not reliable value to afford it in the design stage although if Zs is met it wouldn't do any harm to fit a 'C', they cost the same.
 
Regardless of all the impressive technical explanations I've found changing type B's for C's where GU10's are fitted has dramatically reduced or even eliminated nuisance tripping when lamps fail.....Good enough for me.
 
Regardless of all the impressive technical explanations I've found changing type B's for C's where GU10's are fitted has dramatically reduced or even eliminated nuisance tripping when lamps fail.....Good enough for me.

quite possibly. just because we 're not sure exactly why something works, doesn't mean it don't work. it could just be that the short duration fault current is below the trip threshold of a type C.
 
Re' GU10 50watts, i stopped using them yrs ago, they are anergy hungry, high temp' running and added to this they have this nuisance tripping issue attached LED equiv's are now getting affordable and ive yet to have a customer refuse them because of the extra cost, its all about sales pitch and showing them the real benefits in the long term....

Although im having difficulty getting inrush details of LED lamps and recommended no's per type 'b' or 'c' as manufacturers haven't fully tested them to their products.
 
i don't think inrush current, if any , of a 5 or 7 watt LED is going to trip anything. unless you're using milliamp breakers.
 
Its inductive loading, agree with one or two but when you start getting several or more switching on together you'll be supprised at the combined surge it creates, im waiting on mcb manufacturers spec but they already said there will be a limit dependant on type of mcb, im pretty sure others have already posted with this very problem when having a large no' off LED's switching together and we are not talking 'silly large'
 

Reply to b type or c type in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
191
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Indeed, that was my thought, a B20 having a 60A instantanious trip should easily cover a inrush for a domestic fridge, and if the fridge and...
Replies
11
Views
556
  • Question
That's really helpful. Thank you so much, I will take a look.
Replies
2
Views
1K