Hi Guys,

I cannot see B2 in the tripping curves for 60898 in the BGB, any of you guys know the answer before I ask the manufacturer.

Thanks in advance

Gary
 
page 301in bgb. look at the ones there. for 2A start at the bottom at 10A. draw vertical line to 10sec, then sketch curve parallel to the 6A curve to give a pretty accurate guide.
 
Oh I see, we are presuming all is linear, i.e every B type MCB needs 5x it's rated current to trip in 0.1 to 5 seconds. So I need 10A of fault current for a 5 second disconnection time.

230v / 10A = 23 ohms as a maximum Zs.

Sorted. Can't believe I didn't see the correlation, Thanks telectrix
 
Oh I see, we are presuming all is linear, i.e every B type MCB needs 5x it's rated current to trip in 0.1 to 5 seconds. So I need 10A of fault current for a 5 second disconnection time.

230v / 10A = 23 ohms as a maximum Zs.

Sorted. Can't believe I didn't see the correlation, Thanks telectrix

Type B 60898 MCB 32A or less = 0.1 Seconds disconnection time
Type B 60898 MCB more than 32A = 5 Seconds disconnection time

Type B will require 3 to 5 times load to trip always work on worst case so x5 and so for a 6A 60898 MCB 30A is required for 0.1 second disconnection time as for ZS it will be 230/30 (the 30 being 6A X 5 =30A) = 7.66 and then rule of thumb for temperature rise so 7.66 x 0.8 = 6.13 ZS=6.13 for a 6A circuit. The disconnection times only apply to TN systems.
 

Reply to B2 Tripping curve? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
541
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
918

Similar threads

Indeed, that was my thought, a B20 having a 60A instantanious trip should easily cover a inrush for a domestic fridge, and if the fridge and...
Replies
11
Views
529
Evening all, Just after a sense-check before I commit & send the quote. I’ve been asked to run in an SWA to feed a small CU that’ll sit inside...
Replies
0
Views
156

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top