Oh I see, we are presuming all is linear, i.e every B type MCB needs 5x it's rated current to trip in 0.1 to 5 seconds. So I need 10A of fault current for a 5 second disconnection time.
230v / 10A = 23 ohms as a maximum Zs.
Sorted. Can't believe I didn't see the correlation, Thanks telectrix