Hi, hope one of you guys/girls can helpView attachment PDU backup.pdf. Im working on a project, the schematic is attached. PDU/A is supplying the load in normal operation, if PDU A fails then PDU/B needs to supply the load until PDU/A is operational again. The client doesn't want PDU/B connected to the UPS system at all! I need some way of PDU/B to be automatically powered then non-powered?????? I dont think an ATS is the answer here. Note: only 1 PDU to operate at any one time.
 
If the 2 risers are fed from different supply points, then you can use the other riser to supply PDU/B going through a form of control hook-up between PDU/A and PDU/B

There are several ways of switching ''in'' and switching ''out'' PDU/B, the problem is the speed in which it is accomplished, as the loads are computer servers!! You really need the speed of a ''Static Switch'' .... I'll leave the sourcing etc, to others here that can help you more easily than i.
 
Well, thanks for that. At least i know the answer is not immediatley obvious. Think i'll find and look at the full schematic.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Back-up power
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
Marxman99,
Last reply from
Marxman99,
Replies
2
Views
858

Advert

Back
Top