R

rob1967

Got a Ze reading of 33.1 OHMS on a TT system and a PFC of 1.8KA....All the R1+R2 readings are very good but all the ZS readings are between 16.4 and 17.8 OHMS.....

I know on a TT system you can have a reading upto 1667 ohms but only on circuits upto 32 Amps.....Trouble is I have 16 circuits and 6 of them are over 32 Amps.......

They are all proceted by 30ma RCDS....please can anyone advise? Thanks..


Also, the garage supply has lost the earthing so cannot do a R1 + R2 test on that circuit, fuse board in garage is fine and there is a seperate Earth rod for it.........is this accecptable????
 
Last edited by a moderator:
Got a Ze reading of 33.1 OHMS on a TT system and a PFC of 1.8KA....All the R1+R2 readings are very good but all the ZS readings are between 16.4 and 17.8 OHMS.....


Also, the garage supply has lost the earthing so cannot do a R1 + R2 test on that circuit, fuse board in garage is fine and there is a seperate Earth rod for it.........is this accecptable????


Is this supply cable double insulated tails ,if not, how is it protected from earth fault ?
 
Is this supply cable double insulated tails ,if not, how is it protected from earth fault ?


From the board in the house it's A 6mm pvc/pvc then at the garage end it's SWA into a metal conduit but can only see the caables and not the Armour........Cable lookes to be Alu and not copper.....Have done a Insulation resistance test and it reads at >299........Done a R1 + Rn instead of a R1 + R2 and it reads 0.20 ohms .........Circuit that supplies the Garage is protected by a 30ma RCD..............:confused:
 
Last edited by a moderator:
If this is so then why does it say in Table 41.5 that the Zs readings are for Final circuits not Exceeding 32Amps :confused:

Yes have to agree it does say that but when the first ammendment to 7671 (2008) is issued the words Final circuits not Exceeding 32Amps will be omitted

And a new column created for final circuits exceeding 32A and distribution circuits this value is still 1667 ohms.


This to me shows it was mis wording in the first instance
 

Reply to Bad ZS readings in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
155
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
969
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
That 'stranded 2.5mm' was probably imperial 7/.029 which is about 2.9mm2. Which might account for expected readings being different.
Replies
6
Views
427
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top