R
rob1967
Got a Ze reading of 33.1 OHMS on a TT system and a PFC of 1.8KA....All the R1+R2 readings are very good but all the ZS readings are between 16.4 and 17.8 OHMS.....
I know on a TT system you can have a reading upto 1667 ohms but only on circuits upto 32 Amps.....Trouble is I have 16 circuits and 6 of them are over 32 Amps.......
They are all proceted by 30ma RCDS....please can anyone advise? Thanks..
Also, the garage supply has lost the earthing so cannot do a R1 + R2 test on that circuit, fuse board in garage is fine and there is a seperate Earth rod for it.........is this accecptable????
I know on a TT system you can have a reading upto 1667 ohms but only on circuits upto 32 Amps.....Trouble is I have 16 circuits and 6 of them are over 32 Amps.......
They are all proceted by 30ma RCDS....please can anyone advise? Thanks..
Also, the garage supply has lost the earthing so cannot do a R1 + R2 test on that circuit, fuse board in garage is fine and there is a seperate Earth rod for it.........is this accecptable????