Hi
Is it agree to put power cable and data cat6 on the same cable tray .One side power cable in trunking other side cat6. it's 15 cm separation between them.what separator should be use?
Thanks for help
 
If both cables are screened then you don't have to.

If both are not, then 200mm at a minimum.

Any other combination has different distances depending on the type of divider and wether it's grounded or not.

Search EMC directive, there is table in there which gives you all the particulars.

Don't know if 7671 gives any distances or not to be honest.
 
That makes sense it dado trunking and the likes but no so much on tray I guess.

I'm sure a reg number will follow very soon!
 
528.1 ;)
Seems to demand physical partitioning on tray for cat6 mixed with general LV cables.

Whenever I have been involved with tray systems, the data has its own tray, or sometimes basket.
 
That because 'general' LV cables and cat 6 are not screened?

EMC directive states the info in my first post, I was looking at it a few weeks back.

So for the benefit of the OP, yes it does. How far depends on other factors. Look for the table I spoke of.
 

Reply to Band 1 and band 2 separation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
273
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
267
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

They are excellent, I have used them a few times for consumer unit relocations! They can get a bit tight with cables if you're using all the...
Replies
5
Views
397
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top