The older Schneider DB's 3phase had exposed busbars at the rear of the main switch where it linked from the switch to the main carriage, a cover protected them at the front but anyone pushing cables behind would lead the risk of shorting out the phases with only the upstream OCPD to protect them, the risk is very high if you shove T&E behind before sleeving the earth, modern versions of the DB now have been designed so this cannot happen anymore. I've seen it done many yrs ago where the main switch turned into an electrical fire ball as the front end was the cutout which had been bodged.