As far as business is concerned it is a very good reason why the supply cannot be disconnected.(not 'convenient' is not a reason)
However, when conducting a PIR/EICR, verification of the protective system to the distribution boards and final circuits is achieved by the measurement of the earthing system connected since this is what its there for. You wouldn't expect to have a real fault under test conditions would you?
There are those 'purists', when doing a PIR, who believe the only way to test final circuits is to isolate each one in turn and live test separately. That method might be Ok for a small installation where you have total and continual control of the isolation process, but this is very rarely the case and so other suitable methods have to be used to assess the worthiness of the protective systems. Zs/Zdb is one method.