Basic domestic testing Qs | on ElectriciansForums

Discuss Basic domestic testing Qs in the Domestic Electrician Forum area at ElectriciansForums.net

N

newtothis

I'm just look for confirmation thoughts on this first point.

I think when IR testing on an existing installation and it’s not practical to remove all vulnerable equipment. I can connect L to N to earth and test at 500V on the circuit I’m testing.


The question is if I do the above, could it result in, or contribute to; the measured ZE + R1+R2 not equalling the measured ZS ?


In my case it’s the downstairs RFC it includes the kitchen. It's hard to without causing a bit of damage to access a FCU with a neon to the cooker hood which has an extractor fan and 4 light bulbs.

Thanks in advance for any help, and there's no need for undue diplomacy, or softly softly language, if I'm barking up the wrong tree. :bucktooth: I'd rather know straight !
 
I'm just look for confirmation thoughts on this first point.

I think when IR testing on an existing installation and it’s not practical to remove all vulnerable equipment. I can connect L to N to earth and test at 500V on the circuit I’m testing. (Yes this is acceptable)


The question is if I do the above, could it result in, or contribute to; the measured ZE + R1+R2 not equalling the measured ZS ? (Not sure what you mean by this)


In my case it’s the downstairs RFC it includes the kitchen. It's hard to without causing a bit of damage to access a FCU with a neon to the cooker hood which has an extractor fan and 4 light bulbs. (The FCU should be accessible)

Thanks in advance for any help, and there's no need for undue diplomacy, or softly softly language, if I'm barking up the wrong tree. :bucktooth: I'd rather know straight !

See my replies in Blue mate. :)
 
Thanks for your reply, appreciate it mate !
(Not sure what you mean by this)

I'll use my cooker radial as an example all measured values
[FONT=&amp]ZE 0.14ohm TNS R1+R2 0.12ohm ZS is 0.67ohm should it be 0.26ohm or close.
Tearing what little hair I have left out LOL

Added
6-2.5 mm2 cable
32A Type B MCB

I know the R1+R2 is right from looking up the OSG - 10.49 PM it tallies with the length of the cable.

Checked the ZE several times.
[/FONT]
 
Last edited by a moderator:
IR testing is a test to ensure the IR complies, it will have no bearing on RI+R2 these are the resistances of the line conductor and the cpc in series added together using a low resistance ohmmeter, continuity on you MFT
 
Put a Q in blue :)


Isolate the MCB. Then test from the isolated side of MCB and Live supply side of RCD. This way you are performing the exact same EFLI test except bypassing the RCD so a high current test can be carried out which is more accurate.

The line is connected to earth at the end of the circuit. So you have a PD between the isolated Circuit breaker and the 230 on the supply of the RCD.
 
Last edited:
what was confusing me is I knew it was a live test, and the supply L side is live even if the board isolated.

So in summary, can I say if my measured ZS doesn't exactly equal (or is a significantly out) with my R1+R2 + ZE
Using the low current ZS test can be a factor, along with user error on the testing and loose connections, poor design on the circuit ?

Failure on the IR test is not a contributor to the above, if it's down to something that should have been disconnected?
 
Generally a low current loop test is not that accurate and it is better to perform a high current test whenever possible.

If anything, the measured Zs would normally be lower than the calculated value due to parallel paths via bonding etc.

User error could play a part and not making good contact on the terminals when carrying out the test could contribute to higher than calculated reading.
 
Thanks very much Simonslimline, I'm driven to get this right. I'm going to slow down and double check everying I do.

I have mates who are sparkies and seem mega competent. They admit their knowledge of testing is a bit sketchy.
I'm also working with sparks at the moment who are very well up on testing, but don't take too seriously.
Telling me stories about skipping parts of the testing cos they didn't like the person they were testing for etc etc...
I'm laughing with them at their stories, but inside I don't agree. :teeth_smile:
 
Thanks very much Simonslimline, I'm driven to get this right. I'm going to slow down and double check everying I do.

I have mates who are sparkies and seem mega competent. They admit their knowledge of testing is a bit sketchy.
I'm also working with sparks at the moment who are very well up on testing, but don't take too seriously.
Telling me stories about skipping parts of the testing cos they didn't like the person they were testing for etc etc...
I'm laughing with them at their stories, but inside I don't agree. :teeth_smile:

Sadly you will see this when onsite, depending where though i guess. I have seen this attitude and it all comes down to wanting to be finished faster and being a lazy T@£$%.
If it's there --- in court then its there problem i guess.

Personally i couldn't sleep without knowing i had done my job correctly and verified the safety of my work.

Chris kitcher does a great book on Inspection & testing, well worth a purchase.
 
Last edited:
Remember when testing Zs normally you are also testing through the RCD and the MCB which are not included in the Ze test or the R1+R2 test and occasionally these items can exhibit a noticeable added resistance to the test. This may be what you are experiencing.

A poor design of circuit would not contribute to a variance between ZS and Ze+(R1+R2); if the circuit were poorly designed then they would both be high.

An IR test failure would not affect a Zs / ZXe(R1+R2) variance, although a really bad fail where any conductors were touching could reduce the measured value in both cases; although other factors would come into play before you could do the live test!:sorcerer:

A small diagram for the alt Zs test.
Alt Zs bypassing RCD.jpg
 

Reply to Basic domestic testing Qs in the Domestic Electrician Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks