Only metallic pipework entering the bathroom may need to be supplementary bonded ,as close as possible to where it enters.It matters not whether there is continuity on the pipework once within the bathroom.If plastic pipework coming into the bathroom goes to copper there is no need to bond.
There is no need to supplementary bond if all circuits within the bathroom are RCD protected,and there is continuity of less than 1667 ohms between metallic pipework entering the bathroom and conductive (earthed) parts within the bathroom.
There seems to be this misunderstanding coming up regularly that bonding is to earth the pipes...IT IS NOT.
Bonding is to reduce the risk of a potential difference between metallic sevices entering a building or in this case bathroom, which may introduce an earth potential,and conductive parts connected to the earthing system. The risk of introducing an earth potential comes from OUTSIDE THE BUILDING/BATHROOM,that is why bonding must be carried out as close as possible to the point of entry. Once inside the building/bathroom the pipework is not going to introduce outside earth potential so it can have as many plastic fittings on it as you like.
Perhaps you owe your plumber an apology.