R

revolt3k

Do taps, wastes, and towel rails supplied by plasic pipes need to be bonded if protected by a 30mA RCD in the 17th?
 
Do taps, wastes, and towel rails supplied by plasic pipes need to be bonded if protected by a 30mA RCD in the 17th?

What is protected by the 30mA rcd ?........If you mean All the circuits within the Special location{Bathroom etc], then supplementary bonding may be omitted providing disconnection times are met...main bonding is in place and the pipework is in reliable contact to the M.E.T.




spark1
 
Can someone confirm if you also have to measure the resistance from the cpc of every final circuit within the special location down to extraneous conductive parts etc, with your meter set on the low ohm range. Reading to be <1667 ohm`s in order to omit supplementary bonding.
 
Havn't got ol' red to hand but found this.

In a building with a Protective Equipotential Bonding system in accordance with 411.3.1.2, supplementary EB may be omitted where all of the following conditions are met:

1. All final circuits of the location comply with the requirements for ADS according to 411.3.2.

2. All final circuits of the location have additional protection by means of an RCD in accordance with 701.411.3.3 (ie 30ma / 40ms at 5x)

3. All extraneous conductive parts of the location are effectively connected to the PEB according to 411.3.1.2.

Note: The effectiveness of the connection of extraneous conductive parts in the location to the main earthing terminal may be assessed, where necessary, by the application of 415.2.2.


415.2.2 (in part)

Confirm that the resistance between simultaneously accessible exposed conductive parts and extraneous conductive parts fulfills the following condition:

R is less than or equal to 50 V/Ia,

where Ia is the operating current of the protective device:

for RCD's, I delta n.

for overcurrent devices, the current causing automatic operation in 5s

Should clear it all up for you.;)
 

Reply to Bathroom Bonding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
The chances of any problem without the RCD are minimal, including it extremely negligible......with the supplementary, on a kin to Hannibal Lector...
Replies
6
Views
750
Although the gas pipe may no longer require the bonding, it should really be terminated correctly or completely disconnected at the other end...
Replies
2
Views
439

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top