A customer of mine wants a bathroom fan installing but on its own pull cord so they can control when it is on and off. No run on time required just on and off. Is it ok to come straight off the lighting circuit in the bathroom and use the pull cord as the means of isolation for the fan?
 
It's OK coming off the lighting, (so long as it has RCD protection) but it wouldnt be isolated when turned off via the pull cord would it?
Does it need local isolation?
BS7671 doesnt require local isolation except for emergency switching.
 
Last edited by a moderator:
It's OK coming off the lighting, (so long as it has RCD protection) but it wouldnt be isolated when turned off via the pull cord would it?
Does it need local isolation?
BS7671 doesnt require local isolation except for emergency switching.

Probably not. According to the IET Electricians Guide to the B. Regs page 74 "An extractor fan supplied from a lighting circuit for a bathroom without a window should have it's own means of isolation" they then go on to say so it is not being maintained in the dark i.e. if you turn the 6A lighting breaker off. I take this to mean, given that the bathroom I am working on does have a window, that it does not need local isolation.
 
Probably not. According to the IET Electricians Guide to the B. Regs page 74 "An extractor fan supplied from a lighting circuit for a bathroom without a window should have it's own means of isolation" they then go on to say so it is not being maintained in the dark i.e. if you turn the 6A lighting breaker off. I take this to mean, given that the bathroom I am working on does have a window, that it does not need local isolation.

Do building regs apply in this situation ? It would be wise however to supply a DP FCU for this fan.
 
It's OK coming off the lighting, (so long as it has RCD protection) but it wouldnt be isolated when turned off via the pull cord would it?
Does it need local isolation?
BS7671 doesnt require local isolation except for emergency switching.

There have been many threads on the subject of isolation for extractor fans. I think the main concensus is that the MCB in the CU would meet the regs (not great practice though), however, in this case where the fan will not be on an overun timer a DP pull switch could act as isolation, you could use one such as this PULL SWITCH CRABTREE DP 16amp with p/light | eBay.
 
Last edited:
As an eBay Associate we earn from qualifying purchases.
The building regulations would apply to any alteration of a fixed service.
Whether it would be notifiable to building control is dependent on the locations of the wiring (in or out of zones), but the installation of a fixed speed independent intermittent extract fan is not notifiable.

For the fan the manufacturers instructions very often ask for double pole isolation of the supply, which can be done as HHD says above with a DP pull cord, if they also require the supply to be fused down then a fuse should also be installed.
 
The building regulations would apply to any alteration of a fixed service.
Whether it would be notifiable to building control is dependent on the locations of the wiring (in or out of zones), but the installation of a fixed speed independent intermittent extract fan is not notifiable.

For the fan the manufacturers instructions very often ask for double pole isolation of the supply, which can be done as HHD says above with a DP pull cord, if they also require the supply to be fused down then a fuse should also be installed.

Could you expand on that please Richard ? This goes against my current understanding of the building regs that they only apply where building work as defined by the building regs is taking place.
 
Could you expand on that please Richard ? This goes against my current understanding of the building regs that they only apply where building work as defined by the building regs is taking place.
I would agree with your statement that the building regulations apply to "building work".
However as extracts from the regulations show below the alteration of an electrical fitting is "building work".
However there is a limitation on requirements (8.) that appears to negate Part P, but if that were the case then the approved documents would be pointless (hmmm!)
Schedule 1 is the parts of the building regulations.


2.—(1) In these Regulations, unless the context otherwise requires—
…..
“building work” has the meaning given in regulation 3(1);
…..
“controlled service or fitting” means a service or fitting in relation to which Part G, H, J, L or P of Schedule 1 imposes a requirement;


Meaning of building work
3.—(1) In these Regulations “building work” means—
(a) the erection or extension of a building;
(b) the provision or extension of a controlled service or fitting in or in connection with a building;....





4.—(1) Subject to paragraph (2) building work shall be carried out so that—
(a) it complies with the applicable requirements contained in Schedule 1; and
(b) in complying with any such requirement there is no failure to comply with any other
such requirement.





7. Building work shall be carried out—
(a) with adequate and proper materials which—
(i) are appropriate for the circumstances in which they are used,
(ii) are adequately mixed or prepared, and
(iii) are applied, used or fixed so as adequately to perform the functions for which they are designed; and
(b) in a workmanlike manner.





Limitation on requirements
8. Parts A to D, F to K, N and P (except for paragraphs G2, H2 and J7) of Schedule 1 shall not
require anything to be done except for the purpose of securing reasonable standards of health and
safety for persons in or about buildings (and any others who may be affected by buildings, or
matters connected with buildings).



 
As you say, clear as mud and apparently contradictory.
If the building regs applied to all alterations of electrical equipment and services, all altered switches and sockets in dwellings would need to be at the heights prescribed in part M ?
 

Reply to Bathroom Extract Fan Isolation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
180
Not to mention welding switch contacts together and wondering why when they thought they had got the wiring sussed the light will still not switch...
Replies
5
Views
557

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top