My client wants a wall fitted extractor fan for their bathroom. Normally i fit the isolator outside above the door but the client is against this. Is there any reason why it can not go above the fan at high level so zone 3.
I can not find anything saying you can not but i can not find anything saying i can apart from zone 3 needs to be IP 21.
 
I was under the impression that all switches, in a domestic situation had to be placed at a maximum high of 1200mm to the top of the switch from finished floor level.
How about a pulled core fan isolator.
 
If it is for isolation for maintenance purposes then it must be located so it remains in the control of the person working, or it needs to be capable of being locked once isolated.

Outside the room would not generally comply with this requirement to my mind.

There has been no zone 3 in a bathroom since 2008.
 
That is why I feel it is important to install a fuse connection unit as well as an isolator on bath room fans, then if you are working on it you are able to remove the fuse to lower the risk of the circuit be turned on,
[automerge]1576445615[/automerge]
 

Attachments

  • image.jpg
    image.jpg
    63.5 KB · Views: 40
My client wants a wall fitted extractor fan for their bathroom. Normally i fit the isolator outside above the door but the client is against this. Is there any reason why it can not go above the fan at high level so zone 3.
I can not find anything saying you can not but i can not find anything saying i can apart from zone 3 needs to be IP 21.

Why do you fit them above the door? That makes them an awful eyesore and so obvious.

Why not just fit it at socket height the same as you would the isolator for anything else in the bathroom like a towel rail or jacuzzi bath?
 
Run the bathroom on its own dedicated circuit, that way any work to be done in the room (lights, fans, shaver socket, towel rail etc) gets locked off at the board.
bad idea. you'd be working on the fan without light. OK in daylight hours if there's a window. then again, what are head torches for.?
 
Have to say although it's getting stick on here I often put them high level above the light switch on the wall (level with top of architrave) as a preference, I think it looks neat and is less likely to get switched off by accident. As for it being turned on while you are working on the fan I can't see that really unless you're working down the other end of a massive bathroom and there's an idiot on the prowl!
 

Reply to the thread, titled "Bathroom Extractor fan isolator location" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Bathroom Extractor fan isolator location
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13
Unsolved
--

Thread statistics

Created
philipbg,
Last reply from
robd,
Replies
13
Views
5,481
Back
Top