Continuity is the cause of danger and the need for bonding.What do you mean?
Continuity is the cause of danger and the need for bonding.
It would be better if ALL the pipes entering a bathroom were fitted with isolating plastic sections (ideally a bit longer than a plastic elbow) then all the pipework in the bathroom would be electrically isolated.
No earth paths, no touch voltage, no bonding - definitely no bonding, no worries.
So, when you have a pipe which has been electrically isolated then purposely connecting it again MAY be reintroducing hazards which had been removed.
But not isolated parts - door handle, toilet roll holder.What are you on?! Continuity is exactly what we need to EQUALISE the potential between all extraneous and exposed conductive parts.
No potential between 230V on the basin tap and isolated toilet roll holder either.230V on the bath tap and 230V on the basin tap means no potential difference between them and no belt if touching them at the same time.
Should be no need to bond water pipes at all then.A lovely little idea these plastic isolating sections! How are you planning on isolationg the rather conductive liquid running through them though???
......If sparks do not understand the basics of earthing and bonding then they should consider going on a refresher course.
Removing the connection to earth, if possible, would be preferable.I'm done, I can't have a debate with someone who's against preserving an effective connection to earth through a PVC join.
Connecting a part to earth is not supplementary bonding.The regs are black and white when it comes to supp bonding.
Parts are extraneous because they have a connection to earth in which case they may require bonding.Every extraneous and exposed conductive part in a room containing a bath or shower shall have an effective connection to earth,
If they are not connected to earth (>23kΩ to MET) then they should not be earthed - it would not be bonding.if any don't have this, it needs supp bonding.
That could be so which is why I said 'MAY' in my previous post but reconnecting to earth without testing is incorrect.That PVC join under the bath tub doesn't isolate the taps from earth, it just makes it a poor connection. Solution? Bond it, simples.
There shouldn't be.There's no argument to be had.
Removing the connection to earth, if possible, would be preferable.
Connecting a part to earth is not supplementary bonding.
Parts are extraneous because they have a connection to earth in which case they may require bonding.
If they are not connected to earth (>23kΩ to MET)
Fence sitter!![]()