Bathroom wiring

hi, been asked to do a small job for a customer, im puttin a light inside his shower but instead of having the light switching with other lights in the bathroom he wants it switching when he pulls the pullcord for the shower... to do this i was going to break into the cable going from the pullcord to the shower with henley block then out to a fused spur, from ther with a bit of 1mm cable fused at 3amp to the light, does this sound ok?
 
yes i have explained this but he wants the light on with this pullcord, if there is any safety issues i will be wiring all lights off the lighting circuit but just checking to make sure all would be safe before i done this
 
he can't have it from you, that is the answer,tell him it contravenes the regs and you're not prepared to do that under any circumstances, and if he really wants a cowboy to do his installation then he will have to find his own and suffer the consequences
 
if the shower circuit operated the coil,the the shower would not be on it's own dedicated circuit, therefore the light would have to operate the coil making the contactor cumbersome to say the least, I still think sourcing a light with a proximity switch, or fitting a proximity/pir switch to operate the light is the simplest and most economical ,bearing in mind any regs to be overcome as in siting of a separate proximity switch
 
The only reference i'm aware of, to that is on page 161 of the OSG section 8.5
section simply says that water heaters fitted to storage vessels having a capacity of 15litres or more....... should be supplied by their own separate circuit.
A shower wouldn't apply to this however.

Obviously the restriction to the circuit dedicated to the shower would be the current rating of the MCB or RCBO and cable size for the safe operation of the shower. For 1 shower light it's irrelevant. The impossibility would be trying to get 2 10mm conductors into a shower switch or spur terminal. You could as you said use a 2 pole 100A connector block.
It's simply not good practice though.
PIR is a better option.

I'd be happy to be corrected if i'm wrong. I couldn't find anything specific in BS7671 either
 
Last edited by a moderator:
Just get rid of the pull cord and run two separate ccts in bathroom to a double switch outside the bathroom. One operates the shower light and extractor fan and the other controls the other bathroom lights.......simple for u and customer gets what they want in a roundabout way!
 