Adrian Sadler
Evenin all
Just after opinions on the following...
1. Bedroom turned to bathroom. No cpc in lighting. Boiler in bedroom. Shower in downstairs bathroom. Old mcb board with no rcd....
My view - install rcd to ring main feeding boiler. Spur off this to get good elec for lighting with lv timer fan. Fan isolator. Light n fan fed from spur in loft tagged off ring as stated. Extend shower cable to new location. Install rcd at board for shower. Oh n boiler next to bath so thats being boxed into a cupboard with a lock. Only issue is the fused spur inside the cupboard
Any other ways of doing it differently?
2. Existing bathroom. No isolation for mirror with light n demister. No fuse for fan or lights. Fan is timer model and earth in flex used as switched live. Rcd on board ok. Fan isolator present.
My view - pull lighting circuit back. Install sw fused spur for mirror. Install sfs to cover n protect fan.
Any other thoughts?
Just after opinions on the following...
1. Bedroom turned to bathroom. No cpc in lighting. Boiler in bedroom. Shower in downstairs bathroom. Old mcb board with no rcd....
My view - install rcd to ring main feeding boiler. Spur off this to get good elec for lighting with lv timer fan. Fan isolator. Light n fan fed from spur in loft tagged off ring as stated. Extend shower cable to new location. Install rcd at board for shower. Oh n boiler next to bath so thats being boxed into a cupboard with a lock. Only issue is the fused spur inside the cupboard
Any other ways of doing it differently?
2. Existing bathroom. No isolation for mirror with light n demister. No fuse for fan or lights. Fan is timer model and earth in flex used as switched live. Rcd on board ok. Fan isolator present.
My view - pull lighting circuit back. Install sw fused spur for mirror. Install sfs to cover n protect fan.
Any other thoughts?