A

ANDREW B

What code would you give for a batten holder in a bath/shower room? I know that its zone dependant but I have been calling a code 2 for zone 1 and 2 even if it’s mounted on the ceiling slightly above 2,25m.
The batten holder then needs to be replaced with an IP rated fitting, this then requires a RDC fitting to the bathroom circuit opening a can of worms that may require a consumer unit upgrade.
On the other hand if an IP light was already installed and all bonding in pace, a code 4 regarding the RCD is all that’s required.

Any thoughts?
 
I would give this a Code 2.

I can't see where you are comming from in that having changed from a battern to an IP 45 fitting then requires an RCD. Desirrable as this is, you can make a "like for like" change without even having to write a MEiWC.
 
I have been calling a code 2 for zone 1 and 2 even if it’s mounted on the ceiling slightly above 2,25m.

If it is mounted above 2,25 meters then its outside the zones !
I would read that general rules apply and no requirement for Ip rating

If I am not missing something or reading the post wrong, then I would say that
it is permited in that location and that we should be wary of imposing our own criteria

Advising or deciding that it could be a danger if the lamp shattered and injury could occur that way may be agreed
Changing the fitting for an enclosed type would be like for like
 
Andrew,

Remember that the zones are measured from the bottom of the bath and not the floor, which will bring the light fitting into zone 2 in many cases. In some instances the light is very marginally outside zone 2 vertically,but personally I would give this code 2 just as you are doing. The lack of an RCD I am assured is code 4 provided there is an RCD for sockets potentially for external use, but going back to the bathroom, if there is no RCD then you will also need to verify the supplimentary bonding. If you have neither an RCD nor supplementary bonding then it goes back to a code 2.

Geoff
 
Last edited:
Remember that the zones are measured from the bottom of the bath and not the floor

Are you quite sure about that?

701.32.3

Zone 1 is limited by:

(i) the finished floor level and the horizontal plane corresponding to the highest fixed shower head or water outlet or the horizontal plane lying 2.25m above the finished floor level, whichever is higher.
 

Reply to Batten lights in bathroom in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Whatever... I awoke this morning ready for an intersting and relaxed day at work at my local branch of the Men's Shed charity. " jobs pending...
    • Like
Replies
0
Views
182
  • Question
ok cheers for the help lads
Replies
7
Views
701

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top