ConH85

DIY
Joined
Jan 14, 2020
Messages
4
Reaction score
0
Location
UK
I’m after some advice. I have a single socket in a bedroom where I’m putting some panelling. On the panelling I’m wanting 2 double usb sockets (one each side of the bed).

First question: Should I install a 20A unswitched flex outlet plate in place of the single socket to feed the 2 double usb sockets with some 2.5mm flex behind the panelling?

Second question: Would I be able to add a fused spur from each double socket to feed a wall hung lamp either side of the bed?
 
The answers depend on whether this existing socket is part of a ring final circuit (32A circuit breaker) or not.
simple enough to extend the ring to both new sockets.

Even if its a radial circuit (16A) supply. Can branch off to wherever you need it.

and dont use flex. Use the proper 2.5mm twin and earth solid cable.
 
first thoughts is if you no longer need the single socket, replace with a 13A Fused connection Unit. then spur off to your 2 new sockets. then a 5A FCU from each new socket for each lamp. ( or just 1 5a FCU from 1 socket to feed bothe lights).
 
It’s a 32A ring main. Sorry, forgot to put that. I would put a 13A FCU in place of the single socket but if the fuse was to go it would be behind the panelling.
 
It’s a 32A ring main. Sorry, forgot to put that. I would put a 13A FCU in place of the single socket but if the fuse was to go it would be behind the panelling.

Either way you need access to the socket or FCU. Just in case there is a fault in future and someone has to get to the area.
Don't hide it behind a panel.
 
IF the existing socket has two cables coming into it, and these are confirmed by testing to be the two legs of a RFC, you could join a short length of 2.5mm2 T&E to them, using maintenance free joints only, you could then close in the front of the existing box with a blank plate, and feed the new cable to a fused connection unit mounted on the new panelling. This doesn't necessarily mean that it has to be mounted directly in front of the old socket, but it should be positioned so as the buried existing cables are still in safe zones, as defined in the regs. Mounting it in front of the old socket will ensure this, but there may be other places it can go as well.
You can wire your new sockets and lights from this fused connection unit, using appropriate sized T&E, once again ensuring it is fitted in the safe zones, if concealed.
As you can see, there's much more to this than you might think at first sight.
 
IF the existing socket has two cables coming into it, and these are confirmed by testing to be the two legs of a RFC, you could join a short length of 2.5mm2 T&E to them, using maintenance free joints only, you could then close in the front of the existing box with a blank plate, and feed the new cable to a fused connection unit mounted on the new panelling. This doesn't necessarily mean that it has to be mounted directly in front of the old socket, but it should be positioned so as the buried existing cables are still in safe zones, as defined in the regs. Mounting it in front of the old socket will ensure this, but there may be other places it can go as well.
You can wire your new sockets and lights from this fused connection unit, using appropriate sized T&E, once again ensuring it is fitted in the safe zones, if concealed.
As you can see, there's much more to this than you might think at first sight.
Great idea. I do have a copy of the regs so I’ll have a look tomorrow. Thanks!
 

Reply to Bedroom socket extension in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
933

Similar threads

Echo above, as someone who's probably similarly inexperienced I have set myself up a per point spreadsheet and whack it all in there. This has...
Replies
9
Views
576
It's a room where someone sleeps, so it's a bedroom. Minimum standards were set in the Parker Morris report in around 1963. Anything built after...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top