16mm 3 core swa single phase clipped direct outside (shaded) on a 63 B type 60898
Do I really mean that the maximum length is 68m, or am I being really thick tonight?
Trying to look at a way of providing more power to an outlet pillar that happens to be the furthest point from the supply cabinet (approx 130m) - the new proposed user says that they will need at least 2 x 32A sockets, possibly a 16A as well
 
16mm 3 core swa single phase clipped direct outside (shaded) on a 63 B type 60898
Do I really mean that the maximum length is 68m, or am I being really thick tonight?
Trying to look at a way of providing more power to an outlet pillar that happens to be the furthest point from the supply cabinet (approx 130m) - the new proposed user says that they will need at least 2 x 32A sockets, possibly a 16A as well
Work out your loading, measure the distance apply the correct formula to get the correct cable size
 
I don't think that I can feasible use greater then 16mm, so I have been trying to reverse engineer it and work out the possibility of getting the people in charge to move the position of where the outlet pillar is, but screaming kids and life is making it hard to think.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Doomed

Arms
-
Joined
Location
Dorset

Thread Information

Title
being thick
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Doomed,
Last reply from
Doomed,
Replies
5
Views
1,675

Advert

Back
Top