Southern Spark

I am starting a rewire of a 4 bed maissonette next week. The meter and original c/u is by the front entrance, but the client wants it moved up to the first floor, which will then be near his front door. I want to keep the supply C.S.A at 25 mm, and obviously I will be incorporating a switched fuse to protect the supply, but I was wondering what is the best type of cable to use... the overall length of run is about 15 - 20 m, it will be run under floor boards for some of the run and coming up the wall in a cupboard. Is it ok to use normal tails for this?? I have never seen it done before like this. In the past I have used 16mm T and E, but like i say, there is a lot of heavy loads on the circuits, so I would like to keep it at 25mm, thanks.
 
I have done this too recently, EDF moved meter from cu approx 20m away, SWA for me was too stiff for some of the route so i fed 25mm tails from 80A switch/fuse unit and 16mm earth and 10mm earth (to bring to bonding back to the new origin rather than the c.u.)
I used 32mm galv conduit with an earth clamp at the points the cable needed to be concealed within the wall, make sure if your running through joists they are >50mm from top and bottom and should be fine, abviously cable tie the single cores and earth together so they are basically a big twin and earth

P.S. 20m of 25mm singles + 16mm earth + 10mm earth = ££££
 
Thanks for the responses so far guys... I was thinking split concentric myself, would this be alright. I have not installed it before. Is it not classed as singularly insulated? I like the sound of bringing it up in a bit of 32 mm galv with a nice set into the bottom of the board. What is split con like to work with? is it easy to run through joists??? thanks a lot guys... I love this place :)
 
I thought split con was dodgy for domestic (but cannot back this up with a definitive reg or post, just remember sommat) - as its not really 'meant' for running through a house, so to speak. Something to do with BS numbers, and it being used by the distributors who have different regulations to adhere to...

I am quite happy to be slapped about the head now by people of much greater knowledge ....

fix bayonets!
 
split conn may work out cheaper than tails and deffo cheaper than SWA its a dawdle to work with so long as its treated with respect its NOT SWA and doesnt like scufing to much
 
Only used it a couple of times in an office block. 35mm feeding about 6 sub boards. After years of mauling SWA’s around I thought I has in heaven using it.

Just a word of warning when you cut the outer serving don’t go to deep otherwise you’ll be slicing the neutral insulation. If you ring the cable at the point you want the serving to end you will hear if your going to deep as there is a melinex binder around the N & E conductors, it crackles if you cut it.

Have fun!
 
There are pukka heatshrink trouser crutch sealing breakout accessories available for concentric cables, although you can if competent, use a standard 3 core heatshrink trouser breakout. I would always use these breakout accessories they seal the cable and give a professional finish to the job. You can use amalgamating tape, but unless you know how to work it, it can end up looking like a pig's ear of a termination. I would always use appropriately coloured heatshrink sleeving on both the neutral and the earth conductors.

A little more expense and a little more time i know, but well worth the effort in the finished terminations. Not really that keen on using concentric stuff mind, much prefer SWA route myself!!
 
I have done this too recently, EDF moved meter from cu approx 20m away, SWA for me was too stiff for some of the route so i fed 25mm tails from 80A switch/fuse unit and 16mm earth and 10mm earth (to bring to bonding back to the new origin rather than the c.u.)
I used 32mm galv conduit with an earth clamp at the points the cable needed to be concealed within the wall, make sure if your running through joists they are >50mm from top and bottom and should be fine, abviously cable tie the single cores and earth together so they are basically a big twin and earth

P.S. 20m of 25mm singles + 16mm earth + 10mm earth = ££££


I would be grateful for clarification of the above.
My consumer unit is to be moved across a double garage. Presently adjacent to the incoming supply and gas meter it is to be connected from the new DNO installed isolator using 10m long 25mm tails and 16mm earth. And yes I can confirm that it's costly.

My question is about the earth connection to the gas meter. Does this have to be run (in 10mm) from the new consumer unit location - another 10m of cable? Or can it be connected to the adjacent incomer where the 16mm for the consumer unit is connected - about 1.5m of cable.

Thanks and regards.
 
Well i run my main bonds back to where the new incoming supply/switch fuse is now located as this now becomes the new origin of the supply (where, in the regs its supposed to be connected to), your consumer unit will no longer be at the origin.
in reality theres probably not an issue with running your bonds back to the new consumer unit, as long as they are all installed pukka, but it sounds like less work connecting them at the incoming supply
 
Last edited by a moderator:
I would be grateful for clarification of the above.
My consumer unit is to be moved across a double garage. Presently adjacent to the incoming supply and gas meter it is to be connected from the new DNO installed isolator using 10m long 25mm tails and 16mm earth. And yes I can confirm that it's costly.

.

You must fit your own fuse on these tails. DNO fuse only covers tails up to 3 meters long. Rcd protection will probably also required depending on installation method
 
Thanks Welchyboy I am now clear that the new origin of the supply will be at the start of the newly created sub-main. Also, thanks for the feedback Tony and Hawk81. Yes the installation will have a switch fuse, sorry I didn't mention it. I should have realised that writing "10 m tails" would sound alarm bells with competent persons.
Cheers.
 

Reply to Best way to extend an incoming supply in the Australia area at ElectriciansForums.net

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
717
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top