Having had our PV installations (mine and dad's) a couple of weeks now, we've had time to get used to living with it etc. and our attention has now naturally turned towards monitoring the system in order to try and make optimal benefit from it.

The installers supplied an OWL basic wireless monitoring device connected via a CT sensor to the live feed coming from the inverter into a spare MCB in the consumer unit. This allows us a convenient, portable indication of how much the panels are generating at any given time - useful given that the inverter itself is housed in the loft.

In order to see our household consumption we purchased separately a second similar device and placed the CT sensor as directed over a live feed coming from the main electricity meter.

After much deliberation and scratching of heads we have come to realise that the indicated consumption on this second device is not ideal due to the inability of these CT sensors to establish the direction of the current flow! Hence it seems we are unable to clearly and conveniently tell when and by how much we are importing or exporting...

So... To my main point.. All of the above has ultimately lead me to the following linked page...

Solar PV Monitoring System | OpenEnergyMonitor

...whereupon there are shown two alternative schematics (about one third of the way down the page) for how a solar PV system - particularly the inverter - may be wired into the household wiring and grid. Our system (like most it seems) appears to be wired as per the type 2 schematic - whereas it would appear to me that for what I would like to achieve, the type 1 layout would seem to be more appropriate. My trouble is, I do not quite follow how the type 1 layout works?? Particularly, what is going on in the "junction block" that still allows the grid, consumer unit and inverter to all be wired together - yet there only be a single direction of current flow in order to make the consumption CT sensor operate as I want for my simple monitoring solution to work?

Obviously I'm no electrician..! Perhaps I'm just being thick, but I don't see it.

Can someone please explain? I'd really appreciate it.

Thanks in advance.
 
Last edited by a moderator:
Wouldnt you not be better spilting your tails from the electric meter, fitting an Henley block and giving the inverter and associated generation meter its own direct feed. This way a sensor on the tails going to the CU would give true useage and a monitor accessing the figs from the Inverter itself would give the generation figs to save you going in the loft ??
 
Last edited by a moderator:
Wouldn't you not be better spilting your tails from the electric meter, fitting an Henley block and giving the inverter and associated generation meter its own direct feed. This way a sensor on the tails going to the CU would give true useage and a monitor accessing the figs from the Inverter itself would give the generation figs to save you going in the loft ??

I think that is essentially the type 1 diagram mentioned in the link provided by Mozzer? That's how I have mine wired with a junction box (Henley block) two CT sensors and monitors, one on the CU feed and one on the feed from the inverter. What it doesn't give you of course is the amount exported - and i don't think that's possible with a CT sensor as they can't sense current direction.

My trouble is, I do not quite follow how the type 1 layout works??
This is my non-technical understanding: The current from the inverter flows to the junction box. Depending on house demand, it then either:
- If house demand exceeds what the panels are producing, the "solar current" "joins" the current coming from the mains via the electricty import meter and flows into the house via the Consumer Unit (fuse box) to satisfy house demand. Thus less current is required to flow through the electricity meter from the external mains to support house demand.
OR
- If house demand is less than what the panels are producing, some "solar current" flows into the house to satisfy house demand; the rest flows out through the electricity meter and out the house onto the external mains supply. Thus current flows out through the electricity meter from the house to the external mains. The electricity meter probably either runs in reverse :)rolleyes2:), displays RED or a different coloured LED to indicate 'reverse current'. Either way it records no electricity use.
 
Last edited by a moderator:
Fact:- Only your generation meter will tell you how much you are generating from the inverter ( whether used internally or not ) therefore in theory, the only way you exactly know what you are exporting as "surplus to the house's needs" in any point in time ( real time only ) are by taking the actual sensor reading on the CU tails ( total energy used by house regardless of its origin ) and substracting what you know you have generated as recorded on the GEN Meter at that moment in time. The difference given its a positive no is the theoretic export surplus. You cant use your Electric meter reading as that if OLD may go backwards, plus that only records amount of electric coming into the house to make up the difference for when your PV installation is unable to supply demand.

If you can get a monitoring to system to do this automatically thats great, but worthless info really as at the moment all Energy providers pay you 3p for 50% of the total generated meterage anyway..... !

I record daily;

1. What is generated from the GEN meter

2. The reading on the Electric Meter ( DNO )

3. The reading my Energy Monitor says I used in the house in total regardless of origin ( sensor on the CU tails )

As explained above, with this information you can workout a few things.....................
 
Thanks to all... I get how it works now!

Essentially we are splitting the connection between the Inverter and the DNO Electricity meter - where, currently with my set up, the two are simply connected together via a spare "way" on my Consumer Unit. Splitting out the CU and the DNO Electricity Meter by way of the Henley block allows a single direction of current flow to be moitored whereas with my current set up, it doesn't!

What it doesn't give you of course is the amount exported - and i don't think that's possible with a CT sensor as they can't sense current direction.

Well surely, if the reading on the CT sensor that is indicating panel generation (tapped between the Inverter and the DNO Electricity Meter) is indicating MORE than the CT sensor that is indicating houshold consumption (tapped between the inverter and the Consumer Unit) then you are exporting by the amount of the difference between the two?

Right, where's my neon screwdriver!!... :)

Thanks again!
 
Thanks to all... I get how it works now!Essentially we are splitting the connection between the Inverter and the DNO Electricity meter - where, currently with my set up, the two are simply connected together via a spare "way" on my Consumer Unit. Splitting out the CU and the DNO Electricity Meter by way of the Henley block allows a single direction of current flow to be moitored whereas with my current set up, it doesn't!Thanks again!

To be precise..... you spilt the tails (+/-) which would normally leave the Electric Meter ( DNO) and go straight to the CU. A Henley block sits in the middle which spilts the tails (+/-) from the DNO Meter into two supplies ( for want of a better expression )

One for the CU and the other ( dedicated ) for the PV Install
 
Last edited by a moderator:
Gotya! Thanks. For some reason, my brain could only absorb it from the point of view of the PV generation coming in - rather than from the Grid! Then again, I'm dyslexic! haha.
 
Well surely, if the reading on the CT sensor that is indicating panel generation (tapped between the Inverter and the DNO Electricity Meter) is indicating MORE than the CT sensor that is indicating houshold consumption (tapped between the inverter and the Consumer Unit) then you are exporting by the amount of the difference between the two?
That's true - but only real time. I really meant you can't record the amount exported that day/week/month unless you have a way of continuously recording the difference between the two.
 
Ah I see your point... Although again only true for the most basic of the CT based monitors like my OWL one that was put in by our PV installers. The second CT monitor I bought was one of these:-

Current Cost - Reducing your energy bills so you can live a greener life!

... Which a) hold 7 years worth of historical data, and b) can be connected to your PC and the data graphed or uploaded to the likes of pvoutput.org - all of which was not fully possible with the way my system has initially been wired, hence my OP question.

By the way, these particular Current Cost meters are available new on EBay for around £10 to £15 as they are the same ones that are (or were) being given away free by Eon to their customers - many of whom it seems are selling them on. I've already bought two of these for the princely sum of £22 in total... Happy days.
 

Reply to Best way to wire Inverter to Household/Grid for easy monitoring? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar threads

Welcome to Accelleo! We are excited to present an excellent opportunity for Electronic Engineers to work within the Security and Defence space...
Replies
0
Views
2K
  • Question
Hi Gingerrubix, The fact that your previous Tenant replaced a faulty socket plate which he used for an external EV, raises an eyebrow. Also your...
2
Replies
25
Views
3K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top