bigd

Dear All,

What are the 'tricks' to a good earth rod impedance?

If I'm getting 30-40 ohms am I doing OK?

Am I flogging a dead horse trying to get it any lower?

I know the regs recommend under 200 ohms but what's the general concensus on what constitutes a good reading?
 
Im not the TT guru, but here goes:

The easiest way to get the lowest Ra (resistance of the electrode, and cable to it) is to go deep,. The deeper the better. This is because as you go deeper, the moisture content in the soil increases, and becomes less dependant on the weather conditions. Also the ground wont freeze.

If you hit rock, the the other option is to use another electrode position. This must be sited at least the distance equal to the depth of the longest of the electrode away. So say you have an electrode of 6m depth. The nearest you could place another electrode is 6m away.
You could lay tapes or mats ect to try and lower your reading, but youd have to dig a deep hole, and you probably wouldnt get a much better result than a deep rod. Rod thickness doesnt have a great influence on the resistance, neitrher does the copper content. Rust doesnt have much of an effect either, as it will conduct better than the soil around it. As long as the connection from the cabl;e to the rod is non corroding, then thats ok. We use Denzo tape/paste at work.
The last resort is soil conditioners, but they will undoubtably be expesnive (ive never used them), and i reckon thatb you would have to reapply at set intervals to maintain a low Ra.
 
I would be happy with 30-40 ohms as long as there is no risk of drying out, deeper is better as suggested before. I have put rods into sandstone by drilling holes and putting rods in through a bentonite slurry. Got Ze down to 70 Ohm but with bonding to metal work included it came down to less than 50 Ohm. 20kg of bentonite cost approx ÂŁ20 and I still have lots left, will probably have lots left when I retire. Don't forget that the supply earth resistance can be a max of 21 Ohm but it is not uncommon to get a Ze below 10 Ohm.
 
Im not the TT guru, but here goes:

The easiest way to get the lowest Ra (resistance of the electrode, and cable to it) is to go deep,. The deeper the better. This is because as you go deeper, the moisture content in the soil increases, and becomes less dependant on the weather conditions. Also the ground wont freeze.

If you hit rock, the the other option is to use another electrode position. This must be sited at least the distance equal to the depth of the longest of the electrode away. So say you have an electrode of 6m depth. The nearest you could place another electrode is 6m away.
You could lay tapes or mats ect to try and lower your reading, but youd have to dig a deep hole, and you probably wouldnt get a much better result than a deep rod. Rod thickness doesnt have a great influence on the resistance, neitrher does the copper content. Rust doesnt have much of an effect either, as it will conduct better than the soil around it. As long as the connection from the cabl;e to the rod is non corroding, then thats ok. We use Denzo tape/paste at work.
The last resort is soil conditioners, but they will undoubtably be expesnive (ive never used them), and i reckon thatb you would have to reapply at set intervals to maintain a low Ra.

That's a fair enough answer for a domestic installation Johnyboy!! ...lol!! Though i doubt if he's gone down 6m though!! If he had, he'd probably be a lot lower than the 40 ohms he has now, if the ground soil type is half decent...lol!! But your right Depth is is going to give the biggest gain, not only to the Ra value, but also to the stability of the system...

Also remember that extended rods will always improve over time as the ground compresses around the areas where the couplers have made a slightly larger diameter hole, during driving the rods in.

You only need to maintain chemical enhances, as these tend to leech away over time, You shouldn't need to re-apply the likes of Bentonite, and magnotite (Furse-chem), which are both a surface area increaser, not enhancers as such, but they would rarely be used in a domestic situation...
 
here we go again..
:lipsrsealed2:
ps.read the can...very apt
[ElectriciansForums.net] Best Ze for Earth Rod
 
Last edited by a moderator:
Best Ra reading ive ever had was 0.89 ohms and was on a house which had a soak away where the rod was installed which was connected to a utility room waste ,it had 2 1 meter rods joined together and had an earth rod pit to make access easier never got dry and always had some soapy water entering it which helped the readings
 

Reply to Best Ze for Earth Rod in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top