Hi Chaps...
Just a few questions need a bit of help on please, just completed PIR on TT system this morning:
1/ BS3871 mcbs? Code 4 ?
2/ Readings on ring : r1=0.57 rn=0.57 r2=0.20 ? Any idea what may have happened here, somebody done a bit of an alteration maybe ? Code 2 ?
3/ Zs lower then Ze, strange ? Is this possibly to do with parallel paths ?
4/ Max permissible Zs for a TT system, would I be correct in thinking I use the value from 51.4 = 1667 (there is a 30mA/100A rcd in line)
5/ The property was thatched :
cables in loft next to thatch not mechanically protected ? Any code ?
T5 fluorescent hung in loft 300mm from thatch ? Any code ?
mr16 recessed down lights in bathroom ceiling backing into loft, non fire rated - no hood ? Code 1 ?
Many Thanks Sy
Just a few questions need a bit of help on please, just completed PIR on TT system this morning:
1/ BS3871 mcbs? Code 4 ?
2/ Readings on ring : r1=0.57 rn=0.57 r2=0.20 ? Any idea what may have happened here, somebody done a bit of an alteration maybe ? Code 2 ?
3/ Zs lower then Ze, strange ? Is this possibly to do with parallel paths ?
4/ Max permissible Zs for a TT system, would I be correct in thinking I use the value from 51.4 = 1667 (there is a 30mA/100A rcd in line)
5/ The property was thatched :
cables in loft next to thatch not mechanically protected ? Any code ?
T5 fluorescent hung in loft 300mm from thatch ? Any code ?
mr16 recessed down lights in bathroom ceiling backing into loft, non fire rated - no hood ? Code 1 ?
Many Thanks Sy